how to calculate the megger values for motors and cables?
Answers were Sorted based on User's Feedback
Answer / murali
thumb rule 1KV we get 1Mohm. if suppose 415V motor we get 0.45Mohm.
Megger is the instrument name. it is insulation resistance value.
| Is This Answer Correct ? | 4 Yes | 1 No |
Answer / pradyumna171
megger value of any appleance should be 2 multiply with working voltage in kv plus 1 ie a 440 volt motor should have 1.88Mohm (2* .440 +1) , it is the minimum value. And megger voltage should be twice of working voltage of appleance.
| Is This Answer Correct ? | 2 Yes | 1 No |
which type of motor is suitable for water suction pump ?
What is corona ? Mention its positve effects .
what are the shades for mimic diagram i.e for 3.3kv,6.6kv,11kv,22kv and 33kv? which is the IS for mimic diagram?
What is the unit of charge and current?
How earth fault & earth leakage equvpment are works?
A mass of 1200g is accelerated at 200 cm/s2by a force. The value of the force required is:(a) 2.4N(b) 2400N(c) 240 kN(d) 0.24N
transformer losses
why transformer rating in kva ?
in case of OC+EF relay, how the burden is divided/calculated/shared by the CTs in case of normal (healthy condition) and during fault conditions.? three coils of OC & ef coil is conected in residual connection across the three CTS.
explain single phase series motor
can we connect transformer with star conected secondary to delta connected primary in series?
What do you mean by an instrument transformer?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)