How to take of Transformer oil Break down voltage test?
Answers were Sorted based on User's Feedback
Answer / pillay
i assume your question is how to take transformer oil for
breakdown voltage test.
the sample is taken from the oil drain cork. the containers
and any other equipment used for this job must be ensured it
is dry and not contaminated or this contamination will
influence the oil test results.
1. The sample is connected from the drain cork through a
small hose to a syringe. the initial oil is not taken. from
the syringe the oil is transfered to a sample bottle slowly
without forming air bubbles or too much external atmospheric
contact.this oil is used to test for the dielectic breakdown
voltage in a special tester.the minimum breakdown voltage
depends on the operating systems voltage and local
regulations.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / shaikh
Hi Pillay! can you explain why initial sample of oil is not
taken and what amount of oil is requied for testing?
| Is This Answer Correct ? | 0 Yes | 0 No |
how to calculate voltage regulation?
how we calculate capacitor bank mvar for 11 kv distribution networ , and i need releation between capacitor bank with voltage, frequency, current, pf
what is the earth current,reverse power,electrical trip generator short circuit,low voltage, high voltage please discribe me
what is zero sequence curr ent ?
There are 2 motors without name plate and terminal but one is DC motor and another is induction motor.How one can identify which one is DC and which one is AC motor?
What are the weight of 800KV DA,DB and DC type tower ?
synchronous motor of 13.5MW having which type protection? and how to set relay?give me relay setting calculation for different protection for this motor assume efficiency,power factor and other term if neccecery
What is working principle of washing machine?
how to calculate the power loss of cable?
what is the advantage of using 3 phase line rather than using 2 phase line?
my motor rating is 800HP, 128Amps, 3.3kV. What is capaitor bank i can use for PF improvement to 0.990?
every motors written in name plate IP 55 what is this?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)