What will be the effect of in HT XLPE 220 KV
cable when one side of the Armour/cable ends are not
grounded. Will there is difference between 3-phase voltages?
like: if
A. Both End of Cable grounded Phase Voltages:- V1=219 KV,
v2=220 Kv, v3=220 KV.
B. One End is grounded other is not: than Impact on Phase
Voltages:- V1= KV, v2= Kv, v3= KV. Remain same or
unchanged??
Answers were Sorted based on User's Feedback
Answer / hemant
mostly we consider that armour is given for machanical
protection to cable from any type of hard punching on cable
and other if cable get damaged then it touch to armour
which alredy connected to ground hence our differantial
reley get pick up and device which connect to ht cable is
protected. if both end of armour is connected to ground
there may not any effect to supply voltage in cable it
depend upon cable insulation. only leakage current get
discharge via armour to ground. hence in point of me trere
is no one effect on 3 phase voltage it also remain same.
one thing is that armour one end require to connect ground
and second to device for earthing to device.
Is This Answer Correct ? | 2 Yes | 1 No |
Answer / mahendar kumar
In my opinion Phase voltage would be affected due ungrounded
one end cable.
Is This Answer Correct ? | 2 Yes | 2 No |
Answer / k.prakashchandra
You have measured voltages with the help of PTs located near
the earthed cable ends . As there is a slight difference in
capacitances of the three cables to the Armour(probably due
to unequal lengths) and impedance of the PT is higher than
that of capacitance of the cable ,the neutral is decided by
the capacitances.There is no difference in actual voltages
but there will be a slight difference in measured voltages
Is This Answer Correct ? | 0 Yes | 0 No |
what is meant by impedance & transient protection?
60 watt bulb and 1500watt iron which device has more resistance & why
what are inherent currents?
how can we minimize the off load losses of a distribution transformer which is required to be energized 24x7 ?? capacity of the T/F is 1250 KVA and off load losses are around 2.0 KW.. can we use capacitor bank at the secondary of such a T/F to overcome off load losses? please elaborate briefly...thanks
what are doing the duall connetion in tree phase 10hp or etc motor with circuit diagram
WHAT IS THE SETTING OF OVERLOAD RELAY AND UNDER VOLTAGE RELAY IN PERCENTAGE?
why distribution transformer are of DY11 type?
What is the power rate of power transformer?
How to take Vector group test of Transformer?
16 Answers Sunflag Steel, Zuari Cements,
what is the value of current and voltage that our body can resist ?
What is an ideal transformer?
What is real time power factor control panel(RTPFC)?