What will be the effect of in HT XLPE 220 KV
cable when one side of the Armour/cable ends are not
grounded. Will there is difference between 3-phase voltages?
like: if
A. Both End of Cable grounded Phase Voltages:- V1=219 KV,
v2=220 Kv, v3=220 KV.
B. One End is grounded other is not: than Impact on Phase
Voltages:- V1= KV, v2= Kv, v3= KV. Remain same or
unchanged??
Answers were Sorted based on User's Feedback
Answer / hemant
mostly we consider that armour is given for machanical
protection to cable from any type of hard punching on cable
and other if cable get damaged then it touch to armour
which alredy connected to ground hence our differantial
reley get pick up and device which connect to ht cable is
protected. if both end of armour is connected to ground
there may not any effect to supply voltage in cable it
depend upon cable insulation. only leakage current get
discharge via armour to ground. hence in point of me trere
is no one effect on 3 phase voltage it also remain same.
one thing is that armour one end require to connect ground
and second to device for earthing to device.
Is This Answer Correct ? | 2 Yes | 1 No |
Answer / mahendar kumar
In my opinion Phase voltage would be affected due ungrounded
one end cable.
Is This Answer Correct ? | 2 Yes | 2 No |
Answer / k.prakashchandra
You have measured voltages with the help of PTs located near
the earthed cable ends . As there is a slight difference in
capacitances of the three cables to the Armour(probably due
to unequal lengths) and impedance of the PT is higher than
that of capacitance of the cable ,the neutral is decided by
the capacitances.There is no difference in actual voltages
but there will be a slight difference in measured voltages
Is This Answer Correct ? | 0 Yes | 0 No |
what difference between tapping -15% to +5 % and -5% to +15% tap. & how can define HV turns on maximun & minimum tap of power transformer.
why electron not flow in open loop,how they know path is open ?
single sphase energy meter measur
define the non synchoronism of synchoronous machine in general g or m??
how does an energy meter works?
3phase lt motor winding how to checking with megger
What is an ac motor?
if a damaged 500kva transformer with %impedance 2.6 is replaced by two transformers of 250Kva with different % impedance will they be able to catter the load. what will be the ratio of load on the two transformers if the % impedance is in the ratio 1:2
WHAT IS THE THUMBRULE FOR FINDING OUT THE CURRENT CAPICITY OF A COPPER WIRE?? 2.5, 4, 6MM SQUARE ETC...
difference between slippring induction motor and Generator?
Is LV shorted in magnettic balance test?If yes why?
ple send to the how to improve the efficiency & economical to the thermal power plant