What will be the effect of in HT XLPE 220 KV
cable when one side of the Armour/cable ends are not
grounded. Will there is difference between 3-phase voltages?
like: if
A. Both End of Cable grounded Phase Voltages:- V1=219 KV,
v2=220 Kv, v3=220 KV.
B. One End is grounded other is not: than Impact on Phase
Voltages:- V1= KV, v2= Kv, v3= KV. Remain same or
unchanged??
Answer Posted / hemant
mostly we consider that armour is given for machanical
protection to cable from any type of hard punching on cable
and other if cable get damaged then it touch to armour
which alredy connected to ground hence our differantial
reley get pick up and device which connect to ht cable is
protected. if both end of armour is connected to ground
there may not any effect to supply voltage in cable it
depend upon cable insulation. only leakage current get
discharge via armour to ground. hence in point of me trere
is no one effect on 3 phase voltage it also remain same.
one thing is that armour one end require to connect ground
and second to device for earthing to device.
| Is This Answer Correct ? | 2 Yes | 1 No |
Post New Answer View All Answers
how the CT and PT is connected in the circuit during testing of transformer explain with diagram
Draw the vector diagramme for Asynchronous Induction Generator at noload,half load and fullload.
what is the difference between "Rotary bypass isolation switch and Normal bypass switch" pls share indepth techs?
Why we use Electrical energy rather than any other type of energy, mostly? Explain behavior of open secondary CT and short circuited secondary PT in energized condition?
WHAT ARE THE EFFECTS OF SERIES RESONANCE AND PARALLEL RESONANCE ON THE CIRCUITS PARAMETERS?
What is the unit of charge and current?
An impedance of 100 ohms resistance and an unknown inductance is connected across the capacitor. The resulting impedance is a pure resistance of 500 ohms ifω = 10^5 rad/sec. calculate the values of inductor and capacitor.
How to calculate the multiplying factor for energy meter with ct ratio given
Why syn. Generators are used for the production of electricity?
it is possible to measurement of tension of slipring induction motor(SRIM)carbon brushes, any maesuring instruments are available in the markets.
How will polarity test of Dy5 Transformer ?
what are factors to be consider to design a HT & LT motor?
On what principle electric motor works?
In India the supply voltage is 230 volt A.C. During the negative half cycle phase becomes neutral and neutral become phase? or what will happen during negative half cycle? how the electrons flow during positive and negative half cycle?
how to setting voltage RTCC panel