Why we are using 4-20 mA as Analog signal transmission
other than 3 to 19 or 2 to 18 or 6 to 22 like wise ? What
is the reason behind using 4 & 20 mA? Can anyone give
proper technical reply ?
Answer Posted / vinoth
the destination of any signal will be a Controller.
Take DCS, its input supply will be 1-5V.
from instruments, across a 250ohm resistor, the value will
reach DCS as desired 1-5V.
expl:
say 4ma is the output of transmitter.
V=IR,
V=4ma * 250 ohm
V= 1V,
say 20ma,
V=20ma*250ohm
V=5V.
| Is This Answer Correct ? | 10 Yes | 1 No |
Post New Answer View All Answers
Please can anybody help for control valve sizing step by step procedure?
what is Best Among SINK Or SOURCE Type Design In Digital Signal, Either Iput Or Output? WHY?Can any one..
1.what is controller proportional gain 2.what is the controller intergral action time. 3.A proportional plus derivative controller that has a proportional band of 20% and a derivative action time of 0.1 minutes. Construct the shape of the output waveform for the triangular input if the input rises and falls at the rate of 4 units per minute.
what is your eligibility criteria for freashers?
can we create an interrupt in plc through scada?
How to convert mmWc(mili meter water colam) to tph(ton per hour)?
What are the charcterstics of a P&ID controller block for Governor speed raise or lower for a load sharing functionality between 4 Gas turbines in droop mode.
what is instrument philosophy
Describe how to use megger to measure the earth resistance and insulation resistance
what is actual drum level and compensated drum level?
draw the block diagram of a level transmitter ?
how many pulses are required by a ac induction servo motor of 4 poles with 50 Hz frequency to rotate by 1 degree?
in valve is constructed as per SME B 16.34, then which standard is used for fire testing of valve?.
what is difference between fork type and capacitance type level switch. where it is using
What is PDS and PDMS ?