A Generator is in running condition and Rotor earth fault
alarm is coming.How to check on line(i.e in running
condition) whether there is actual earth fault in rotor or
not.
Answers were Sorted based on User's Feedback
Answer / kk
Rotor earth relay have 2
stage. One 4 alarm & other 4
trip. One can check the
bridge o/p voltage(mV) &
compare with comissioning
time value.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / bhuvnesh kumawat
rotor earth fault alarm comes only if our carbon brushes
become earthed. it may be at the time of changing carbon
brushes.
Is This Answer Correct ? | 1 Yes | 3 No |
Answer / sujeet kumar
we have to check the status of zero sequence relay..
if its not affected then there is not any earth fault
Is This Answer Correct ? | 0 Yes | 5 No |
Answer / alok
rotor both side earth fault wire open and check countinuti
with the help of multimeter at rotor both end.but one side
wire who is grounded must be grounded.
Is This Answer Correct ? | 2 Yes | 8 No |
what is the problem of generator over voltage.?except automatic voltage regulator card
In any plant or substation main incommer voltage RY - 415 V,YB - 400 V, BR - 387 V(in commer feed from transformer 11 Kv /0.415 KV) why found voltage differance in each phase? plant have not self power plant it is depend on outsource grid
what is tertiary winding in transformer?What is its purpose?
what is a drive ?
If the soil resistivity is more large, how can we earthing our 11 k.v. transmission line?
What will be the minimum megger value of 1700 KVA Transformer? a) Do megger value varies according to climate conditions and area . b) If megger value is 100 mega ohm is it good for new transfomer. Explain?
Why slip-ring and brushes are not required in squirrel cage induction motor?
i am in need of AC SYNCHRONUS MOTOR 30KW. ANY ONE KNOWS THE MANUFACTURER OF SAME. ALSO MOSFET AC CONVERTER 20KVA CONT.OUTPUT.
Why SF6,VCB,Oil Ckt Breakers are use in HT Side need brief information ?
if main CT is of ratio 50/5, and meter CT is -/5 what will be overall multiplying factor of meter.PT is 11000/110 .
If you don’t have coal, salt and copper, then how would you earth your connection temporarily at a camp site.?
For a 500 MVA 400/220/33KV transformer following data given HV power = 500 MVA IV power = 500 MVA LV power = 5 MVA If input power is 500 MVA then how output power is (500+5)MVA. Can anyone help