hi
i have a 400kva transformer
i want to know the test i can use to check on it
thx
Answer / binod
as the transformer capcity small so only megger value can
decided to make it on.IF STAR/STAR CONNECTED THAN ALL STAR
POINT EARTH REMOVED.IF DELTA/STAR THAN THE STAR POINT EARTH
BE REMOVED.
ph to earth(p)MEGGERED IF SATSFIED
ph to earth(s)MEGGERED IF SATSFIED
PH(P) TO PH(S) MEGGERED IF SATSFIED
VOLTAGE RATIO TEST(PRIMARY HV TO SECONDARY LV)
GIVING LOW VOLAGE TO HIGH VOLAGE SIDE AND MEASURE THE
VOLTAGE IN LOW VOLTAGE SIDE IN ALL PHASE(LINE VOLTAGE AND
PHASE VOLTAGE) IF ALL THE ABOVE VALUES SATISFIED THAN THE
TRANS.MAY BE ENERGISED.
| Is This Answer Correct ? | 1 Yes | 0 No |
Is current scalar or vector?
Construction of ac motor?
how 650 volts creates? where is use?
1 amp means-how many electron flow per second. ?
how many units (kwh) are there if in one MW?
How many turns are there in primary winding? (In Transformer)
Did RMU have ct and pt ?
how many types control panel of a 132/33 kv substation
What are the advantages of hydropower?
when we should use Central Battery system and UPS system and why? in other words, what are the differences between the two systems?
WHY DOES NEUTRAL DO NOT CARRY EVEN THOUGH IT CARRIES RETURN CURRENT?
what is the meaning of the parameters labeled on the surge arrestor like 150/20 ???
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)