hi
i have a 400kva transformer
i want to know the test i can use to check on it
thx
Answer / binod
as the transformer capcity small so only megger value can
decided to make it on.IF STAR/STAR CONNECTED THAN ALL STAR
POINT EARTH REMOVED.IF DELTA/STAR THAN THE STAR POINT EARTH
BE REMOVED.
ph to earth(p)MEGGERED IF SATSFIED
ph to earth(s)MEGGERED IF SATSFIED
PH(P) TO PH(S) MEGGERED IF SATSFIED
VOLTAGE RATIO TEST(PRIMARY HV TO SECONDARY LV)
GIVING LOW VOLAGE TO HIGH VOLAGE SIDE AND MEASURE THE
VOLTAGE IN LOW VOLTAGE SIDE IN ALL PHASE(LINE VOLTAGE AND
PHASE VOLTAGE) IF ALL THE ABOVE VALUES SATISFIED THAN THE
TRANS.MAY BE ENERGISED.
Is This Answer Correct ? | 1 Yes | 0 No |
in dc series motor if field wdg is shorted then
What is the difference bet ween EDO Type & MDO type ACBs, and what is the advantage EDO Type over than MDO type ACBs.
why rating of transformer is in kva instead of kw?
main difference between ac and dc?
what is IDMT relay.
To make a basic instrumentation amplifier, it takes A One op-amp with a certain feedback arrangement B Two op-amp and seven resistors C Three op-amps and seven capacitors D Three op-amps and seven resistors
The following equipment are installed ia a plant 1. 110KW Induction motor 4 Nos 2. 30 HP motor 3 Nos 3 15 HP Motor 3 Nos 4 7.5 HP motor 4 Nos what is total load of plant if one of each is stand by.
why put integration for capacitorand differation for inductance
why reactive power control is required
WHY FEEDERS TRIP IN COLD AND FOGY WEATHER?
i purchase a microwave which is 50/60Hz but Current Setting 60Hz in my country we usually use 50hz, can i use AVR to solve my problem?
How to arrange a hous hold earthing system to keep minimum earth resistance( below 7ohms).