why battery dc voltage become Half when we check with
respect to ground for example 120volts + and - terminals
and when we check + terminal with Earth thats 60volts why
60volts we can not ground the battery.
Answers were Sorted based on User's Feedback
The midpoint of rectifier transformer secondary is
earthed.The potential of ground is taken as +/- 0.The
voltage measured between any terminal wrt ground will be +/-
half the full voltage.This method is helpful to trace a
single polarity and for earth fault locator.
| Is This Answer Correct ? | 6 Yes | 3 No |
Answer / sarvesh kotiyal
Because your Ground is not connected with V-(V- which is taken as reference point). when you check Voltage respect to ground that time you should also check the resistance between V+ to E & V -E which is equal(the Value which is higher than 10 mega ohm ).
Simple apply voltage Divider & you will get half Voltage
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / koti
The value shown is a capacitive value i.e it is due to capcitance effect wyou are getting some value. If you put a lamp it will not glow.
| Is This Answer Correct ? | 2 Yes | 2 No |
The above answer is correct.If you use an earth fault
indicator ,you are able to measure voltages. And if you run
both leads along the ground or a metal surface ,you can
measure voltages with a digital voltmeter ,as the
capacitances between the leads and the surface/ground, bring
the surface/ground to +or- zero potential.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / sarvesh kotiyal
the resistance between the supply and ground is very high(1-5gohm). so Ideally it should not show any voltage but Internal Input resistance of multimeter approx 10 Mohm for Voltage measurement which is almost a short circuit in comparison to earth .so when you check voltage with respect to earth
V + to E = 24 * 10/10+10 = 12 V.
| Is This Answer Correct ? | 2 Yes | 2 No |
i have a Connected Load of 280KW and Maximum Demand of 224KW to one of SMDB under design with me. which criteria should i consider to design panel and main cables connected Load or Maximum Demand 1)Breaker rating 2)Panel Busbar rating 2)Incommer cable sizing (ignore Voltage drop)
why Copper loss is represented as I square R ?
what do you mean by linear and bilateral network?
what is B , c & d curves in MCB characteristics i e Full Form of B , C & D . sir please give me answer
can we connect 2.2kw star motor in delta passion?
why we cant use AC supply products in DC supply?
Please define ampere?
How to check phase R,Y,B
can we use the step down transformer to step up transformer
i want to know about psu exam eligibility critaria?
what is IP55,IP65
WHAT IS EXTENDED DELTA AUTOTRANSFORMER? WHERE WE USE THAT?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)