I do wonder why current is present in neutral wire?i check
single phase lead current feeding air conditioner...on its
phase its current was 10A while same was 10A in neutral...as
we know in neutral voltage is zero so if voltage is zero
then how current appears on amp meter?
my second observation is (just imagination)when I touch
phase wire it give me shock but when i touch neutral nothing
happens although as above its carrying current(amps)
third but with same logic...as in simple Alternate current
sine curve there is + and there is negative peak.means every
time phase changing so how come every time same phase and
same neutral stand
(pardon for english mistakes)
Answer / puneeth kumar
In neutral current should flow, because it is return path. It
is not giving shock or while checking in tester it will not
glow, because current always choose the least path and neutral
is earthed and our body as about 1000ohms (as per IEEE 80).
In neutral always voltage will be zero only, since it will
connected to ground in star point of transformer. Positive and
negative waves will be appearing in phase only.
Check in 2 phase, you will get 2 waves.
Is This Answer Correct ? | 8 Yes | 0 No |
There are Two questions about Steam Turbine Generator... What is HRSG bypass of LP, HP used for in power generation? In particualar, in the event that fault of HP bypass, there would be STG TRIP in operation but none on the LP bypass fault...what's the reason ?
What is Harmonic affects in power system. what is unit of harmonics and how to measure it. how much value should be in power system.
What is icu and ics in Acb and how many time icu or ics passes from breaker?
Pure inductive ckt takes power from AC when 1. Applied voltage and Current increases 2. applied voltage and current decreses 3. voltage decreases and current decreases please justify
Why we should use delta connection in primary and star connection in an distribution transformer, which converts 400v a.c. voltage to 33kv.
15 Answers ABC, Kirloskar, Sify,
When measuring the Insulation resistance of a motor winding (winding to earth) using a megger meter, Applied voltage(1000V) was automatically reduced to 500V. and the measured insulation resistance values are also very low (in Kohm range) Can anyone give me a reason???
what is the difference between synchronous & asynchronous generators
in ac system the current wave form becomes zero for every half cycle then how can we get continuous supply can any one answer to this plsss
Is possible to increase the voltage without using transformer? why?
we have 2.2kw,Y,3000rpm motor but 6leads found in TB what happen if we connect in delta?
How to test Alternator stability test for REF relay
What is the difference between MCCB and MCB ?