how to test a motor from megger
Answers were Sorted based on User's Feedback
Answer / r.kumar
for megger test in motor.......we apply 500v DC supply at terminals and check:
1.phase 2 phase(ohms)
2.phase 2 body (>100MEGA OHMS OR GIGA OHMS)
3.phase 2 neutral(>1 GIGA OHMS)
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / bameshwar
To identify the motor winding is correct or not. Body to coil and coil to coil for identify the motors coils shorted or not. It's values are body to coil-infinity or more than 5megaohms,coil to coil - 0megaohms,and coil to othercoil-we are seeing the insulation between coils
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / bameshwar
To check the winding s of motor is correct or not (motor shorted or ready to run) it's values are body to coil-infinity, and the coil to coil - 0megaohms, & coil to other coil we are seeing insulation between coil to other coil which is according to motor.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / avvsnmoorthy
motor winding meggar value from bofy t0 phase more tham 5
mega ohm &winding to winding 0 with using 500 volts megger
| Is This Answer Correct ? | 2 Yes | 4 No |
How many capacitors using in LT panel as per Govt rules?
how the harmonic pluses take place in the flow of current
The objective of connecting a resistance and capacitance across gate circuit is to protect the SCR against
Iwould like to know barc interview questions
DEAR SIR,I GOT THE CALL LETTER FROM RRB, SECUNDERABD AS A JE-II SO PLEASE PROVIDE ME SOME MODEL QUESTION AND ANSWER PAPERS AND LAST YEAR QUESTION PAPERS
What is the diffrence between an ELCB(earth leakage circuit breaker) and RCCB(residual current circuit breaker)?which has higher degree of safety and why?
To prove the capacity of a 10MVA transforemr with 6.5% impedance by a short circuit test how much power is needed to inject an impedance voltage if we have to arrive for its rated current?
What is the difference b/w chock and ballast?
what is the difference between UPS & Inverter
What is the percentage loss for aluminium wire for HT line more than 11KVa
HOW TO CALCULATE THE HEAT AND LOAD OF LT-SUBSTATION WHICH CONTAINS 2*1MVA TRANSFORMERS,LT-SWITCH BOARD,MLDB,ACB,BUSBAR,ETC,......?
what is meant by slip & where its occur ?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)