why transformer calling in VA rating
Answers were Sorted based on User's Feedback
Answer / murali290
For any device the rating is given based on the losses occur
in it (loss is nothing but heat).In transformer 2 types of
losses occur 1.core losses: which depends on V &
2.cu losses: which depends on I only
but no losses depends on p.f.
therefore trasformer rating proportional to VI or VA
for large transformers the rating in kilo or mega ,hence
KVA or MVA
Is This Answer Correct ? | 3 Yes | 1 No |
Answer / praha tuty
Transformer has copper loss & iron loss. copper loss occur
in windings & it is due to emf.Iron loss occur in core due
to current. so in order to measure the both losses,
transformer ratings are in VA rating.
Is This Answer Correct ? | 0 Yes | 3 No |
Answer / rakesh maharjan
The KW rating is dependent on the power factor and power factor can be different depending the condition where as mostly 0.8, but if KVA rating is given we can calculate the KW rating as per our condition. So KVA rating is fixed and reliable to any malfunciton not to occur. so the transformer rating is given in KVA.
Is This Answer Correct ? | 4 Yes | 7 No |
Answer / pramod attri
it's using step up, and step down at same frequency..by
mutual inductance.. it case transformer calling in kv,,,
Is This Answer Correct ? | 0 Yes | 4 No |
Answer / rajeshambur
transformer have a two losses because open circut and short circut . two losses so transformer rating in va
Is This Answer Correct ? | 1 Yes | 11 No |
WHAT IS A BASIC DIFFERENCE BETWEEN THYRISTOR,TRIAC AND A DIAC.AND WHAT R THERE APPLICATIONS?
why synchronous motor has zero starting ?
How neutral voltage for transformer decided? eg 33kv neutral voltage for 200MVA transformer?
What are RMU yard Safety Operating Procedures
Which device is provided as backup of Buchholz relay???
difference between high and low impedance BUS BAR relay??
does the power factor of an induction motor improve upon used in parallel with a synchronous condenser , used commonly to provide a leading kva ?
why motor run slow speed in star connection?explain how?
What is 100% protection of generator? Why 95% protection is used not 100%?
any one please tell taht what type questions will be asked in BHEL interview, i am having interview on 24th Dec, please send this to mail pradeepsistam@yahoo.co.in
why use only sf6 circuit breker in 400 kv sub station
neutral earth resistance testing is it possible for transformer while in load condition