Can we measure pressure using differential pressure
transmitter? If yes then how?
Answers were Sorted based on User's Feedback
Answer / loganathan
Yes we can measure pressure with the help of Differential pressure transmitter,we have to connect the HP side of the transmitter to the process line where we are going to measure the pressure,But only thing is we can measure only up to the range of minimum since Differential pressure transmitter will be in range om mmwc.
| Is This Answer Correct ? | 17 Yes | 1 No |
Answer / manishahir
we measure pressure using differential pressure transmitter by connect the HP side of the transmitter to the process line and LP side of transmitter should be open in atmospheric.
| Is This Answer Correct ? | 8 Yes | 1 No |
Answer / dhiru patel
Yes,we can use DP tx for pressure measurement for vacuume pressure(absolute PT) and low gauge pressure measurement.It depends on service,pressure range and diaphragm material.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / ayaz
we know that dp transmitter working principle on pressure difference and in dp type transmitter two ranges URV and LRV
1 LRV is low side value and 2 URV is high side value
SO only reed high side pressure this is vessel pressure
or connect the hart comminucator and then display the vessel pressure
| Is This Answer Correct ? | 0 Yes | 1 No |
Answer / johnan
actually we can use the differential pressure transmitter to measure the flow and level, not the pressure, how, if level, it calculate the difference of high side and low side of the transmitter, then it convert to the level using formula,it is a very long explanation,this is only a laymans term...
| Is This Answer Correct ? | 0 Yes | 9 No |
how to calibrate transmitter
What is pressure,What is temperature,What is flow,What is level
why temperature transmitter is showing ambienttemp.but 21.5ma. alarm AO showing at the display &how to sloves this problem.
what is the deferance between LCN and UCN.
how to do dynolab wind speed sensor loop test, how to simulate value,i have simulate mA 4-20mA but not responding in DCS faceplate, please kindly advice me any one.
where uses EXe /EXd/Exo/Exn/Exp/Exq/EXia
can anybody tel me how a vfd or any field instrument communicates/interface with plc/scada/cs.
Is there’s power on the bus (if so, state whether on the signal bus, or on a separate in the following: a) HART b) Profibus DP c) Profibus PA d) DeviceNet e) Foundation Fieldbus
How to convert 0-2500mmH2o into kg/hr? Or how to convert mmH2O into kg/hr,t/hr etc
any body tell me ,contol valve has how many cheractristic? explain it.
Which instrument used to calibrate the pressure switch?
hay friends, i am in trouble to understand PID controller. several times i have study but it is not clear to me have you a simple way to understand.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)