Can we measure pressure using differential pressure
transmitter? If yes then how?
Answers were Sorted based on User's Feedback
Answer / loganathan
Yes we can measure pressure with the help of Differential pressure transmitter,we have to connect the HP side of the transmitter to the process line where we are going to measure the pressure,But only thing is we can measure only up to the range of minimum since Differential pressure transmitter will be in range om mmwc.
| Is This Answer Correct ? | 17 Yes | 1 No |
Answer / manishahir
we measure pressure using differential pressure transmitter by connect the HP side of the transmitter to the process line and LP side of transmitter should be open in atmospheric.
| Is This Answer Correct ? | 8 Yes | 1 No |
Answer / dhiru patel
Yes,we can use DP tx for pressure measurement for vacuume pressure(absolute PT) and low gauge pressure measurement.It depends on service,pressure range and diaphragm material.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / ayaz
we know that dp transmitter working principle on pressure difference and in dp type transmitter two ranges URV and LRV
1 LRV is low side value and 2 URV is high side value
SO only reed high side pressure this is vessel pressure
or connect the hart comminucator and then display the vessel pressure
| Is This Answer Correct ? | 0 Yes | 1 No |
Answer / johnan
actually we can use the differential pressure transmitter to measure the flow and level, not the pressure, how, if level, it calculate the difference of high side and low side of the transmitter, then it convert to the level using formula,it is a very long explanation,this is only a laymans term...
| Is This Answer Correct ? | 0 Yes | 9 No |
diff between neutral ,ground,phase , earthing and shielding?
Specific gravity.
Can anybody please let me know Orifice plate sizing calculation formula and step by step procedure
What denotes the 5/8mm in the 3300XL 5/8mm proximitor probe?
wht is mean by dpt(differential pressure transmitter)
what pressure transmitter?
Explain PID, ON/OFF, Controls
0 Answers CCIE, Gulf Engineering,
why 4 to 20 ma ,why not 0 to 20 or 3 to 15 or anything
19 Answers Honeywell, TCS, TN,
how to write the program for single push button by using ladder diagram
our kks tagging is crossing more than 12 character please suggest how to take tags in the DCS
Where is wet leg is used?
why use 50% lel methane gas concentration for gas detector calibration instead of 60% lel gas concentration whereas the hi alarm set at 60% lel.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)