capillary type tranmitter using remote seals and capillary
tubes filled with liquid of known of known density so if
you wanna callibrate it just close block valve just before
capilary @ high side & connect druck apply it's calibrated
range pressure as normal calibration ensure low side block
valve must be closed & if you asking commissioning so this
is not a DP type pressure tx so simple if you wanna put in
servie this tx just open high side block valve & than low
side block
same way i do it but still transmitter showing -13 ma.just
tell me what i want to do ?



capillary type tranmitter using remote seals and capillary tubes filled with liquid of known of kn..

Answer / carl_ellis

A 2 wire, loop powered transmitter can not output a negative current, like -13mA. The 4-20mA output is always positive.

However, a remote seal DP transmitter used for level will 'see' a negative pressure with nothing in the vessel and the LRV (lower range value) for the transmitter will be a relatively negative value, close to the (negative) span of level range.

A DP transmitter with remote seals used for level measurement will ALWAYS have a zero level reading that is a relatively large negative number because of the head pressure of the fill fluid in the capillaries.

The reason for the negative value is that the fill fluid in the high side capillary (which connects to the lower flange) pulls away from the transmitters high side diaphragm as it presses down on the lower seal by the force of gravity.

Oppositely, the fill fluid in the low side capillary (which connects to the upper flange) exerts a positive static pressure on the transmitter's low side diaphragm because the seal is up high and the fill fluid presses down on the low side transmitter diaphragm, again by the force of the acceleration of gravity.

A differential transmitter works by subtracting the low side pressure from the high side pressure:

High side minus low side = differential

As an example, in a vessel 7m tall, the transmitter has two remote seals, each 4 meters in length. The upper seal has to be above the liquid level in the head space above the liquid. The medium is water, SG = 1.00.

Assume a fill fluid with a Specific Gravity of 1.00, 4m of high side capillary and 4m of low side capillary. With nothing in the vessel (zero level), the applied pressures would be:

high side pressure = approx - 3.75m H2O (negative 3.75 meters, water column)
low side pressure = approx 3.75m H2O (positive 3.75 meters, water column)

high side minus low side = differential
-3.75m minus 3.75m = - 7.5m (negative 3.75m minus 3.75m = negative 7.5m)

The LRV (lower range value) would be approximately -7.5m H2O.

The transmitter needs to be ranged properly, with the appropriate lower range value for zero level.

Carl Ellis
Measure First

Is This Answer Correct ?    1 Yes 1 No

Post New Answer

More Instrumentation Interview Questions

Describe the typical instrumentation used in monitoring the performance of a shell and tube heat exchanger.

0 Answers  


Explain about P&ID diagram?

3 Answers   Technip, Toyo Denki,


how we will install a positioner ?

2 Answers   Descon,


What is expansion of SMART Instruments? And What is it?

35 Answers   Atesco,


can we connect instrument earth pit to electrical earth pit, if not why?

2 Answers  






Exothermic reaction./ endothermic reaction

0 Answers   CCIE,


State four different types of flow measurement.

4 Answers   ADMA OPCO,


what is piezoelectric transducer?give an example in power plant n state its principle?

0 Answers   Jindal,


how to solve temperature error in compressor?

1 Answers  


what is the difference b/w normal thermocouple and skin type thermocouple?

1 Answers   Heisco,


What is surge and how is it prevented, what is the purpose of bypass valve across AS valve.

0 Answers   ADMA OPCO,


I have observed in field instrumentation work... I remove the fuse of an analog transmitter then it shows 7.75 kg/sq cm (which is practically wrong value)in DCS and when put the fuse it shows 0 in dcs. Then cheach the field transmitter termination and found moister. clean that and then it shows 1.1 kg/ sq cm which is right value. Please describe the above phenomenon.

1 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4452)
  • Electrical Engineering Interview Questions Electrical Engineering (16638)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)