Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


capillary type tranmitter using remote seals and capillary
tubes filled with liquid of known of known density so if
you wanna callibrate it just close block valve just before
capilary @ high side & connect druck apply it's calibrated
range pressure as normal calibration ensure low side block
valve must be closed & if you asking commissioning so this
is not a DP type pressure tx so simple if you wanna put in
servie this tx just open high side block valve & than low
side block
same way i do it but still transmitter showing -13 ma.just
tell me what i want to do ?



capillary type tranmitter using remote seals and capillary tubes filled with liquid of known of kn..

Answer / carl_ellis

A 2 wire, loop powered transmitter can not output a negative current, like -13mA. The 4-20mA output is always positive.

However, a remote seal DP transmitter used for level will 'see' a negative pressure with nothing in the vessel and the LRV (lower range value) for the transmitter will be a relatively negative value, close to the (negative) span of level range.

A DP transmitter with remote seals used for level measurement will ALWAYS have a zero level reading that is a relatively large negative number because of the head pressure of the fill fluid in the capillaries.

The reason for the negative value is that the fill fluid in the high side capillary (which connects to the lower flange) pulls away from the transmitters high side diaphragm as it presses down on the lower seal by the force of gravity.

Oppositely, the fill fluid in the low side capillary (which connects to the upper flange) exerts a positive static pressure on the transmitter's low side diaphragm because the seal is up high and the fill fluid presses down on the low side transmitter diaphragm, again by the force of the acceleration of gravity.

A differential transmitter works by subtracting the low side pressure from the high side pressure:

High side minus low side = differential

As an example, in a vessel 7m tall, the transmitter has two remote seals, each 4 meters in length. The upper seal has to be above the liquid level in the head space above the liquid. The medium is water, SG = 1.00.

Assume a fill fluid with a Specific Gravity of 1.00, 4m of high side capillary and 4m of low side capillary. With nothing in the vessel (zero level), the applied pressures would be:

high side pressure = approx - 3.75m H2O (negative 3.75 meters, water column)
low side pressure = approx 3.75m H2O (positive 3.75 meters, water column)

high side minus low side = differential
-3.75m minus 3.75m = - 7.5m (negative 3.75m minus 3.75m = negative 7.5m)

The LRV (lower range value) would be approximately -7.5m H2O.

The transmitter needs to be ranged properly, with the appropriate lower range value for zero level.

Carl Ellis
Measure First

Is This Answer Correct ?    1 Yes 1 No

Post New Answer

More Instrumentation Interview Questions

How we are blocking 40 kg or more pressure through only 6 kg instrument air in control valve 

3 Answers  


What is difference between reset and initialization in system.

1 Answers   Marafiq,


A flange is used for instrument connection for a system with a design temperature of 316&#61616;C (600&#61616;F) and a design pressure of 1000 kPa (145 psi). What is the class rating of the flange to be used for this application? Explain your answer

0 Answers  


What is the difference bitween control net scaner and device net scaner

0 Answers   Binani,


Hi Frnds , If Suppose 1 Pair cable of 1.5 sq mm is used for Transmitter and instead of 1.5 sq mm if i used 0.5 sq mm cable will the resistance change will occur and does it affect our transmitter reading. plz mail ur answer to ntnkamble@gmail.com plz immediately mail ur reply

1 Answers  


you are on site,the plant trips,you are approached by operations,what do you do?

0 Answers   ABB,


Can we use a 10000 Lph Flow Transmitter in 100 LPH flow line to get 20mA O/P by adjusting SPAN ?

1 Answers  


What is DCS?

5 Answers   Adani,


Im having problems with interfase betwen SPI v7.0 and SPPID v5.05. Previous versions of Intools shoul be fixed with SPPIDproj.ocx file. It was necessary to replace this file with one that allows the connection between different versions of SPPID. It is necessary in the current version to do the same?Thanks

0 Answers  


can you suggest good traning institute in instrumentation ? (in automation, or designing)

5 Answers  


i need some objective type questions in instrumentation

0 Answers  


what is output of FOUNDATION FIELD BUS transmitter

0 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)