capillary type tranmitter using remote seals and capillary
tubes filled with liquid of known of known density so if
you wanna callibrate it just close block valve just before
capilary @ high side & connect druck apply it's calibrated
range pressure as normal calibration ensure low side block
valve must be closed & if you asking commissioning so this
is not a DP type pressure tx so simple if you wanna put in
servie this tx just open high side block valve & than low
side block
same way i do it but still transmitter showing -13 ma.just
tell me what i want to do ?
A 2 wire, loop powered transmitter can not output a negative current, like -13mA. The 4-20mA output is always positive.
However, a remote seal DP transmitter used for level will 'see' a negative pressure with nothing in the vessel and the LRV (lower range value) for the transmitter will be a relatively negative value, close to the (negative) span of level range.
A DP transmitter with remote seals used for level measurement will ALWAYS have a zero level reading that is a relatively large negative number because of the head pressure of the fill fluid in the capillaries.
The reason for the negative value is that the fill fluid in the high side capillary (which connects to the lower flange) pulls away from the transmitters high side diaphragm as it presses down on the lower seal by the force of gravity.
Oppositely, the fill fluid in the low side capillary (which connects to the upper flange) exerts a positive static pressure on the transmitter's low side diaphragm because the seal is up high and the fill fluid presses down on the low side transmitter diaphragm, again by the force of the acceleration of gravity.
A differential transmitter works by subtracting the low side pressure from the high side pressure:
High side minus low side = differential
As an example, in a vessel 7m tall, the transmitter has two remote seals, each 4 meters in length. The upper seal has to be above the liquid level in the head space above the liquid. The medium is water, SG = 1.00.
Assume a fill fluid with a Specific Gravity of 1.00, 4m of high side capillary and 4m of low side capillary. With nothing in the vessel (zero level), the applied pressures would be:
high side pressure = approx - 3.75m H2O (negative 3.75 meters, water column)
low side pressure = approx 3.75m H2O (positive 3.75 meters, water column)
high side minus low side = differential
-3.75m minus 3.75m = - 7.5m (negative 3.75m minus 3.75m = negative 7.5m)
The LRV (lower range value) would be approximately -7.5m H2O.
The transmitter needs to be ranged properly, with the appropriate lower range value for zero level.
Carl Ellis
Measure First
Is This Answer Correct ? | 1 Yes | 1 No |
Describe the typical instrumentation used in monitoring the performance of a shell and tube heat exchanger.
Explain about P&ID diagram?
3 Answers Technip, Toyo Denki,
how we will install a positioner ?
What is expansion of SMART Instruments? And What is it?
can we connect instrument earth pit to electrical earth pit, if not why?
Exothermic reaction./ endothermic reaction
State four different types of flow measurement.
what is piezoelectric transducer?give an example in power plant n state its principle?
how to solve temperature error in compressor?
what is the difference b/w normal thermocouple and skin type thermocouple?
What is surge and how is it prevented, what is the purpose of bypass valve across AS valve.
I have observed in field instrumentation work... I remove the fuse of an analog transmitter then it shows 7.75 kg/sq cm (which is practically wrong value)in DCS and when put the fuse it shows 0 in dcs. Then cheach the field transmitter termination and found moister. clean that and then it shows 1.1 kg/ sq cm which is right value. Please describe the above phenomenon.