I have observed in field instrumentation work... I remove
the fuse of an analog transmitter then it shows 7.75 kg/sq
cm (which is practically wrong value)in DCS and when put
the fuse it shows 0 in dcs. Then cheach the field
transmitter termination and found moister. clean that and
then it shows 1.1 kg/ sq cm which is right value. Please
describe the above phenomenon.
Answer / carl_ellis
Reason: ground current added to loop current through a
ground created by moisture.
The analog input on the DCS references ground at some point.
The moisture in the junction box or remote terminal panel
makes a connection to a local ground at that point. The
difference in potentials between the grounds causes a ground
loop - current added to the modulated loop current. The
DCS's analog input 'sees' this current, even though the
transmitter is turned off, because the current is driven by
the potential of the ground loop, not the potential from the
power supply.
When the moisture (and hopefully, the dirt) is removed, the
local ground connection is broken and the loop is isolated,
except for the DCS's AI reference to ground. So the DCS AI
'sees' only the loop current modulated by the pressure
transmitter and reports the correct loop pressure.
Some handheld calibration instruments can detect current
leakage in loop powered loops. An example is the Practical
Instrument Electronics (PIE) 334 Plus calibrator.
http://www.piecal.com/products/evolution/334Plus_mA.php
Carl Ellis
Measure First
| Is This Answer Correct ? | 3 Yes | 0 No |
tell me about Woodward505 Function as a point of Instrument Engineer.
Can I calibrate the Electromagnetic Flow Meter on line and How.
wht is snap action switch?where it is used?is there any diff between snap action switch and normal pressure switch?
what is relation between electronics&instrumentation
How does a strain gauge measure pressure?
How can one improve linearity of an RTD based temperature measurement system?
Which tank weighing system is better to install (Accuracy point of view) 1) Tank weighing system with 3 load cell or 2) Tank weighing system with 4 Load cell
How to calculate mmwc values into tonnes?
What is the formula of vabration sesore. i mean how to covert mils to volt plz share if any body knows very argent : my mai is merajalam143545@yahoo.com
Hi, I am Newely Joined in Construction company instrument engineer? Any one can Plz tell me How can I advanced preparation for Releated Engineering and construction Documents?
Someone please do mail me some instrumentation questions for Hindustan Petroleum test to avinalexander@gmail.com .Really would be gateful if someone could help me
3 Answers HPCL, Immersion, IOCL,
what is proportional & what is proportional band
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)