Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


I have observed in field instrumentation work... I remove
the fuse of an analog transmitter then it shows 7.75 kg/sq
cm (which is practically wrong value)in DCS and when put
the fuse it shows 0 in dcs. Then cheach the field
transmitter termination and found moister. clean that and
then it shows 1.1 kg/ sq cm which is right value. Please
describe the above phenomenon.



I have observed in field instrumentation work... I remove the fuse of an analog transmitter then i..

Answer / carl_ellis

Reason: ground current added to loop current through a
ground created by moisture.

The analog input on the DCS references ground at some point.
The moisture in the junction box or remote terminal panel
makes a connection to a local ground at that point. The
difference in potentials between the grounds causes a ground
loop - current added to the modulated loop current. The
DCS's analog input 'sees' this current, even though the
transmitter is turned off, because the current is driven by
the potential of the ground loop, not the potential from the
power supply.

When the moisture (and hopefully, the dirt) is removed, the
local ground connection is broken and the loop is isolated,
except for the DCS's AI reference to ground. So the DCS AI
'sees' only the loop current modulated by the pressure
transmitter and reports the correct loop pressure.

Some handheld calibration instruments can detect current
leakage in loop powered loops. An example is the Practical
Instrument Electronics (PIE) 334 Plus calibrator.

http://www.piecal.com/products/evolution/334Plus_mA.php

Carl Ellis
Measure First

Is This Answer Correct ?    3 Yes 0 No

Post New Answer

More Instrumentation Interview Questions

What is negative range in transmeter?

1 Answers   TCL,


what is zero and span ?

0 Answers  


why we use 3 wire rtd direct wiring for temperature measurement instead of temperature transmitter like bearing temperature

0 Answers   ABG Energy,


Sir, I want junior executive, Instrumentation question papaer for IOCL, Plz send to arabinda.ghosh83@gmail.com

0 Answers   IOCL,


in a power plant main steam flow is volumetric or mass flow? is it required compensation?

1 Answers   Wartsila,


A PLC is programmed to drive three motors A, B and C as follows : After running motor A for an hour, motor B should get ON and motor A should get OFF. And after running motor B for an hour, motor C should get ON and motor B should get OFF. And after running motor C for an hour, motor A should get ON and motor C should get OFF. (That is, a cyclic repetition with time period one hour) Now, the second condition is: If any motor gone faulty and is tripped, the consecutive motor should get ON and the faulty (tripped) motor should be eliminated from cyclic repetition. The remaining two motors should bear the cyclic repetition of one hour each. (For healthy motor take logic as high and for tripped motor take logic as low) Now, the third condition is: When motor A load(Amps) exceeds 60% of its rated load, motor B should get ON in parallel to motor A. And when both motors A & B are running in parallel, and if their load exceeds 60% of their rated load, motor C should also start in parallel to A & B. [Here the cyclic repetition is eliminated, until their loads become normal(40%)] [Take logic high(1) for load at 60% and logic low(0) for load at 40%] Now draw a flow chart or a ladder diagram to fulfill the above condition.

0 Answers   MNC,


How to convert 4 wire level transmitter connection to 2 wire.

2 Answers  


suppose in dcs range of a flow transmitter is 10t/hr what is dp for 50% in 2500mmwc

6 Answers   Chevron,


How to work ultrasonic flow meter ?

1 Answers  


what is the difference between impact plate n coriolis type solid flow meters n how they works....n which one is better

1 Answers  


if a tank is contaning oil and water than how can we measure the oil and water level seperately

3 Answers  


two common seiling liquid used in seal pots are:

1 Answers   Thermax,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)