I have observed in field instrumentation work... I remove
the fuse of an analog transmitter then it shows 7.75 kg/sq
cm (which is practically wrong value)in DCS and when put
the fuse it shows 0 in dcs. Then cheach the field
transmitter termination and found moister. clean that and
then it shows 1.1 kg/ sq cm which is right value. Please
describe the above phenomenon.
Answer / carl_ellis
Reason: ground current added to loop current through a
ground created by moisture.
The analog input on the DCS references ground at some point.
The moisture in the junction box or remote terminal panel
makes a connection to a local ground at that point. The
difference in potentials between the grounds causes a ground
loop - current added to the modulated loop current. The
DCS's analog input 'sees' this current, even though the
transmitter is turned off, because the current is driven by
the potential of the ground loop, not the potential from the
power supply.
When the moisture (and hopefully, the dirt) is removed, the
local ground connection is broken and the loop is isolated,
except for the DCS's AI reference to ground. So the DCS AI
'sees' only the loop current modulated by the pressure
transmitter and reports the correct loop pressure.
Some handheld calibration instruments can detect current
leakage in loop powered loops. An example is the Practical
Instrument Electronics (PIE) 334 Plus calibrator.
http://www.piecal.com/products/evolution/334Plus_mA.php
Carl Ellis
Measure First
Is This Answer Correct ? | 3 Yes | 0 No |
how to calibrate temprature switch and flow switch ?
Describe all types and levels (4-20mA, 0-10V, mV, pulse, etc.)of analog and digital I/O used in process control application.
Please send the all question with answer related for interview.
how the presure switches are calibrated? and what happen inside?
what is pico fuse? how this different rom othe fuses and how to locate it inside the card?
what is pressure control
1 Answers GNFC, IBM, Privi Organics,
why vortex flow meters and electro magnet flow meters are used in water treatment plants
Why Pressure Transmitter is NOT installed before up-stream of an ORIFICE PLATE? in a flow measurement.
whats the working of principal thermocouple
what is vibration sensor working principal and how many types its has??
i am from instrument branch i want paper patern of mahagenco . any pevious years paper regarding my branch send me please . please.....
How can we calibrate pressure and flow transmitter in the field(online)?