Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


I have observed in field instrumentation work... I remove
the fuse of an analog transmitter then it shows 7.75 kg/sq
cm (which is practically wrong value)in DCS and when put
the fuse it shows 0 in dcs. Then cheach the field
transmitter termination and found moister. clean that and
then it shows 1.1 kg/ sq cm which is right value. Please
describe the above phenomenon.



I have observed in field instrumentation work... I remove the fuse of an analog transmitter then i..

Answer / carl_ellis

Reason: ground current added to loop current through a
ground created by moisture.

The analog input on the DCS references ground at some point.
The moisture in the junction box or remote terminal panel
makes a connection to a local ground at that point. The
difference in potentials between the grounds causes a ground
loop - current added to the modulated loop current. The
DCS's analog input 'sees' this current, even though the
transmitter is turned off, because the current is driven by
the potential of the ground loop, not the potential from the
power supply.

When the moisture (and hopefully, the dirt) is removed, the
local ground connection is broken and the loop is isolated,
except for the DCS's AI reference to ground. So the DCS AI
'sees' only the loop current modulated by the pressure
transmitter and reports the correct loop pressure.

Some handheld calibration instruments can detect current
leakage in loop powered loops. An example is the Practical
Instrument Electronics (PIE) 334 Plus calibrator.

http://www.piecal.com/products/evolution/334Plus_mA.php

Carl Ellis
Measure First

Is This Answer Correct ?    3 Yes 0 No

Post New Answer

More Instrumentation Interview Questions

in any transimitter (flow/level) there are three terminals for supply& test (+,-,+)in two wire,24VDC given to Tx.,but how 4-20 ma signal travels thru same wire (as it is for 24VDC input supply)?

1 Answers   Jindal, UltraTech,


What is an instrumentation amplifier? How is it better than a differential amplifier when handling outputs from a wheatstone's bridge?

2 Answers   Honeywell,


In Safe Guarding test what means by "Failed to Danger" ?

0 Answers   Optimal,


in plc source and sink meaning?

1 Answers   CGL,


How much should be the values and/or percentages of these given below factors for a good controller ? Steady state error Delay Rise Time Overshoot Peak Time Settling Time Damping Oscillations & vibrations thanks

1 Answers  


what is the principal of flow transmeter,level trans meter,presser transmeter?

11 Answers   Nestle, Reliance,


What is Process portal A(PPA)?

1 Answers   ABB,


Hi buddies! i am facing a problem and if someone could help me it will be an immense pleasure to me. we have compect logix PLC 1769 2L AO module to Heat @ 52 to 56 Deg C .So if anyone can do please help me out with this problem.I'll be highly grateful.

1 Answers   Cadila,


What is the function of positioner in control valves? does the control valve operate without positioner?

3 Answers   Hofincons,


How a pH sensor & analyzer work at waste water treatment plant, whats the principle & science is beyond this,How pH sensor sence & convert signal & move toward analyzer & analyzer show reading in percent? also what is temperature compensate option in analyzer

1 Answers  


Why DP transmitters are subjected to high static pressure test of 100 bar. Though they will be used for very small pressure range

4 Answers   HPCL,


what is the formula for calculating milliampere at different pressure points for eg 4-20 ma = 3-15 psi but if i have to check the ma at 4.6 ma?

4 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4453)
  • Electrical Engineering Interview Questions Electrical Engineering (16638)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)