I have observed in field instrumentation work... I remove
the fuse of an analog transmitter then it shows 7.75 kg/sq
cm (which is practically wrong value)in DCS and when put
the fuse it shows 0 in dcs. Then cheach the field
transmitter termination and found moister. clean that and
then it shows 1.1 kg/ sq cm which is right value. Please
describe the above phenomenon.
Answer / carl_ellis
Reason: ground current added to loop current through a
ground created by moisture.
The analog input on the DCS references ground at some point.
The moisture in the junction box or remote terminal panel
makes a connection to a local ground at that point. The
difference in potentials between the grounds causes a ground
loop - current added to the modulated loop current. The
DCS's analog input 'sees' this current, even though the
transmitter is turned off, because the current is driven by
the potential of the ground loop, not the potential from the
power supply.
When the moisture (and hopefully, the dirt) is removed, the
local ground connection is broken and the loop is isolated,
except for the DCS's AI reference to ground. So the DCS AI
'sees' only the loop current modulated by the pressure
transmitter and reports the correct loop pressure.
Some handheld calibration instruments can detect current
leakage in loop powered loops. An example is the Practical
Instrument Electronics (PIE) 334 Plus calibrator.
http://www.piecal.com/products/evolution/334Plus_mA.php
Carl Ellis
Measure First
| Is This Answer Correct ? | 3 Yes | 0 No |
what is cavitation ?
Draw a P& ID showing – orifice flange, plate, dp transmitter, isolation & bypass valves and tubing.
How to Calibrate Flow Switch in field
How to Calibrate Level Switch in field
How a oxygen sensor & analyzer work at boiler or furnace, what’s the principle & science is beyond this, How O2 sensor scene & convert signal & move toward analyzer & analyzer show reading in percent?
1 Answers GS Engineering Construction, KNIC,
what is zenier barier and what means zone 1,zone 2,and zone 3
2 Answers Bapco Bahrain Petroleum Company,
3element
Describe the function of Accumulator into the Pump
how to set calibration range in a DP transmitter to measure level for a closed tank and for an open tank,and also please explain me how to set calibration range for a DP flow transmitter in a line ?
How do you identify between actual alarm and false alarm in a Temperature Transmitter in SCADA based Control System
How will you measure surface temperature of SUN?
Which of the following instruments consumes maximum power during measurement?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)