I have observed in field instrumentation work... I remove
the fuse of an analog transmitter then it shows 7.75 kg/sq
cm (which is practically wrong value)in DCS and when put
the fuse it shows 0 in dcs. Then cheach the field
transmitter termination and found moister. clean that and
then it shows 1.1 kg/ sq cm which is right value. Please
describe the above phenomenon.
Answer / carl_ellis
Reason: ground current added to loop current through a
ground created by moisture.
The analog input on the DCS references ground at some point.
The moisture in the junction box or remote terminal panel
makes a connection to a local ground at that point. The
difference in potentials between the grounds causes a ground
loop - current added to the modulated loop current. The
DCS's analog input 'sees' this current, even though the
transmitter is turned off, because the current is driven by
the potential of the ground loop, not the potential from the
power supply.
When the moisture (and hopefully, the dirt) is removed, the
local ground connection is broken and the loop is isolated,
except for the DCS's AI reference to ground. So the DCS AI
'sees' only the loop current modulated by the pressure
transmitter and reports the correct loop pressure.
Some handheld calibration instruments can detect current
leakage in loop powered loops. An example is the Practical
Instrument Electronics (PIE) 334 Plus calibrator.
http://www.piecal.com/products/evolution/334Plus_mA.php
Carl Ellis
Measure First
Is This Answer Correct ? | 3 Yes | 0 No |
what is Instrumentation?
why we use impulse line of flow transmitter at 45 deg. angle both side of orifice plate.
Can anyone convert a 5/2 way or 3/2 way valve into an ISO valve?
Why Instrumentation Air Compressor called as Instrumentation Air compressor?pls dont just tell its trasferring IA to all transmitter,valves.I need exact reason, please......................
key exchanges in wpa,wpa2,tls
How we are deciding while programming in pid controller , What we are using heating or cooling.
Hi Friends i am going to write BARC written test by this month 20th (20-5-2008). So please if any body knows the details about this or having previous question papers pls mail me to kkumarei@gmail.com. For Suggestions give one message to 9962122264
if i want to make a zero trim for mass flow meter the pipe line should be empty or i need to make it full? i really need the answer pls help me
During the design and engineering of a process plant, a good designer should plan for ____________, ___________ and ____________ aspects of the plant
How to calibrate the magnetic flow meter and how to correct the flow if it is showing more flow.
5 Answers Bohra Industries Limited, TCL,
plz exlain the dcs system of ABB sympony hamnony
What is sensitivity in vibration probes..?