Answer / d.ramesh classes
efficiency of transformer depends on core loss and copper loss. core loss depends mainly on voltage and copper loss depends on current passing through the winding. so basically total loss i.e. efficiency depends on voltage and current that's why we rate transformer in KVA.
by D.RAMESH CLASSES
| Is This Answer Correct ? | 12 Yes | 0 No |
Answer / abhishek maji
Transformers ratings are given in kVA because the operating power factor of a transformer depends on the load,it is not constant rather varies with load...Secondly if it is rated in kW then as the operating power factor is not known in advance so operating current may be more than its rated current which may affect the winding insulation due to additional heating......Thirdly a transformer acts as an interfacing device between the power generating station and the load center and as my load not only demands active power but also requires reactive power so a transformer must have the capability of handling both types of powers.. that's another reason why transformers ratings are in kVA...
| Is This Answer Correct ? | 2 Yes | 2 No |
Answer / lakhan.self
Transformer is a static device which transfer the power from primary to secondry winding without change in frequency. So VA is unit of apperent power by means power is same ie VA in both side so Transformer rating is in KVA.
| Is This Answer Correct ? | 5 Yes | 7 No |
why we don't use earthing as neutral?
What happens to a line-frequency of high-frequency transformer when it is first energized/ re-energize?
what will happened to give the dc supply to ac transformer?
What will happen if induction motor is supplied with capacitive load?
why DC is not generated instead of AC?
how can service sitting be setted for MCCB?Example for sittings IR (CURRENT RATING),IS(CURRENT STARTING)IO (current operating)?
how we can calculate earth fault current?
A distribution transformer giving afrequency of 200HZ, where it is rated for 50HZ. when it will occure?
there is a line fault some where on the ove head distribution line. how will i locate the fault for clearing it? ofcourse i have to megger the line but what information makes me clear that the fault is in that section of the line?
What is metering cubical? What is the use?
What is the function of Fuel and Oil filter in DG.
What is the difference between single core 2 wire and single core 3 wire system? Which application we are using this? and for What purpose we are using this?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)