whytransformers rating in KVA?
Answers were Sorted based on User's Feedback
Answer / d.ramesh classes
efficiency of transformer depends on core loss and copper loss. core loss depends mainly on voltage and copper loss depends on current passing through the winding. so basically total loss i.e. efficiency depends on voltage and current that's why we rate transformer in KVA.
by D.RAMESH CLASSES
| Is This Answer Correct ? | 12 Yes | 0 No |
Answer / abhishek maji
Transformers ratings are given in kVA because the operating power factor of a transformer depends on the load,it is not constant rather varies with load...Secondly if it is rated in kW then as the operating power factor is not known in advance so operating current may be more than its rated current which may affect the winding insulation due to additional heating......Thirdly a transformer acts as an interfacing device between the power generating station and the load center and as my load not only demands active power but also requires reactive power so a transformer must have the capability of handling both types of powers.. that's another reason why transformers ratings are in kVA...
| Is This Answer Correct ? | 2 Yes | 2 No |
Answer / lakhan.self
Transformer is a static device which transfer the power from primary to secondry winding without change in frequency. So VA is unit of apperent power by means power is same ie VA in both side so Transformer rating is in KVA.
| Is This Answer Correct ? | 5 Yes | 7 No |
selection of conductor in different voltage?
How can w select the cable size for different rating load & also waht r factors affecting the during selection of cable?
11 Answers AB Inc, Bosch, BRB Cable, Lucas TVS, Trisome Technical Services,
Is a direct shorth ciruit on a branch MCCB in a Low Voltage Switchboard a correct means of tesing the performance for discrimination?
what is the relation between KVAR,KVA,KW?why we are mentioning capcitor rating in kvar?what is meant by arcing horn and horn gap in transformer?what is equipotential wire?
WHY CURRENT DECREASES WHEN VOLTAGE IS INCREASED IN A CURRENT TRANSFORMER ?
why 3 phase motors are preferable over single phase motors ?
Is it possible to make a 5P10/ CT Ratio 50/1A Burden 5VA
can volts/Hz be relied upon to use 460v,60Hz electric motors on a 380v,50Hz power supply?
In a 3 phase,400v,4 wire system, 2 incandescent lamps, one having 230v,100w and the other 230v,200w are connected between r phase- neutral and y phase-neutral respectively. If neutral wire breaks which lamp will fuse first and why?
Why lightning arrester blast in rainy day?
1 Answers Eco Cement, Mahaveer, MBDL,
What is Vk and Imag i.e Knee point voltage & Magnetising Current? How to calculate above values? How to define accuracy class 5P10?
7 Answers Deccan Cements, Doosan, Torrent Power, Transco,
Can we use a window type neutral CT instead of a bar type neutral CT. We have an issue with a neutral bar type CT of 800/1 ratio with a Circuit breaker NS800L shneider type, and we want to change it with a window type. Pls advise. Thanks
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)