what is relay
Answers were Sorted based on User's Feedback
Answer / sunil shelake
A relay is device that detects the fault and initiates the
operation of the circuit breaker to isolate the defective
element from the rest of the system.
Is This Answer Correct ? | 10 Yes | 2 No |
Answer / thowsif_emerson
A relay is an electrical switch that opens and closes under
the control of another electrical circuit. In the original
form, the switch is operated by an electromagnet to open or
close one or many sets of contacts. It was invented by
Joseph Henry in 1835.
Is This Answer Correct ? | 9 Yes | 3 No |
Answer / mantu
A relay is a sensing device which sense the fault on the
system and gives the trip signal to the circuit breaker.
Is This Answer Correct ? | 5 Yes | 2 No |
Answer / kabilan
relay is act as a switching device &coil energised at the
time contacts are open
Is This Answer Correct ? | 3 Yes | 2 No |
Answer / yuvaraj
Relay is only cut off the unit when flow of current more
than it's range set by electromagnetic contact.
Is This Answer Correct ? | 2 Yes | 1 No |
Answer / mohammed yousuf khan
A Relay is a device which senses the fault in the circuit and sends signal to the Circuit Breaker to break the circuit.
There is a difference between a relay and a circuit breaker, both are entirely different.
In a circuit, duty of Relay is to sense the fault whereas Circuit breaker should break the circuit upon receiving signal from the relay.
In a circuit, Relay as Master and Circuit Breaker as Slave.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / ksnmurthy
relay is having normally close normally oepn contacts are
there so operation wise we can use relay by switching on
and off according to circuit
Is This Answer Correct ? | 0 Yes | 2 No |
How to calculate Grid rotor resistance(GRR) losses in slip ring induction motor?
What is the 415V AC Soft starter? Explain with an example?
Why the transformer rating is denoted in VA rating why not in KW
how to calculate the ac and dc wire losses with calculations plz tell me
If we are given a 10 amp cable type and asked to calculate the number of cores used and the thickness of the cable, how do we do it?? please help...urgent!! i hope the question is clear enough!!
if installing the transformer why put the sprit the stone ?
While performing stability test of differintial cts how to know the voltage and current on both side of the transformer?
I have a current transformer with 1 main reading meter with transformer outside the building and a control panel having 5 CT reading meters with black round coils inside the building. I want to know, A) when current pass through the Transformers, will the current be reduced or be the same and after that B) when current pass through the CT meters with black round coils, will the current be reduced or be the same. C) in the above process will the reading of the main meter be same or different, from the total reading of all the 5 CT meters.
what are the main Parts of VCB
we have 2.2kw,Y,3000rpm motor but 6leads found in TB what happen if we connect in delta?
Explain Analog and Digital signals?
how to calculate the megger values for motor, cables and transformers?