i want to control the temp of sand(welding flux) between the
range of 150deg C to 170deg C. sugges me sum temp control
method without PID controller.
Answer / carl_ellis
An On-off controller with a setpoint of 160 Deg C and a
hysteresis of ±10 Deg C will do this type of control.
Carl Ellis
Measure First
Is This Answer Correct ? | 0 Yes | 0 No |
What is the logic a Transmitter control a Control Valve? How the signal going to the Control valve? What are systems/Panels/cables/signal used to control valve from Transmitter?
Capacitance, resistance ( colour coding ), parallel & series circuits.
In close vessel/ drum why we use d.p. transmitter of -ve range i.e. (-)500 to 0 mmwc.
Consider a level troll. i am getting a correct value in 4mA and 20mA. the value in the middle(30 to 60%)is disturbed and i am not getting the appropriate value. what is the solution to normalize the level and to get the correct value..
IS IT POSSIBLE TO CALIBRATE A LEVEL TRANSMITTER INDICATOR(ABB) USING HART COMMUNICATOR.? I MEAN TO CHANGE FROM ONE UNIT TO ANOTHER WITHIN INDICATOR (EG. INCH TO FEET)...? PLZ NOTE THAT I HAVE MADE THE UNIT CHANGE IN TRANSMITTER USING HART COMMUNICATOR..BUT WHAT ABOUT THE INDICATOR..?
In your own words, would you expect an ultrasonic level device to work better in a pressure vessel with a high pressure or a strong vacuum, and why?
How do bending tubing provide better measurement than using tubing fittings such as elbows?
Identify the electrical variable that is either directly or inferentially used by various instruments to determine the value of a measured variable.
how to calibrate control valves & power cylinders & ultra sonic level transmitters
Pls.could any one Clarify the following with an example. 1.At What condition Close on Rise and Close on Fall Pressure Switch contacts are used. 2.If Pressure is abnormal as per set pressure,if connecting Terminal of pressure switch breaks,how the voltage extends to Relay base. 3.Are these contacts come under fail safe philasaphy.
control panel design guidelines
why magnetic flow meter is not used in thermel power plant operation