when the PFR (POWER FACTOR REGULATOR)change a step to
zero,one of the RCCB will triped off,is it the changing step
of this PFR effect the RCCB?
Answers were Sorted based on User's Feedback
what is a RCCB doing inside a PFR. Any way if a rccb trips
than it means there is a earth leakage.otherwise the wiring at
the PFR is wrong especially the neutral connections or the
RCCB itself is faulty. Check all the wirings first and than
try substituting the RCCB itself
Is This Answer Correct ? | 0 Yes | 0 No |
what is a RCCB doing inside a PFR. Any way if a rccb trips
than it means there is a earth leakage.otherwise the wiring at
the PFR is wrong especially the neutral connections or the
RCCB itself is faulty. Check all the wirings first and than
try substituting the RCCB itself
Is This Answer Correct ? | 0 Yes | 0 No |
What is the difference between online ups and offline ups?
44 Answers Electrical Tech, GMR, Gravity India, HCL, Indus Towers, NIT, Pyramid, Techno Electric and Engineering, UBS,
what is the relationship between current&voltage in practical purpose ?
how do i work out the Amps of a incommer if i am running 1 37 KW motor and a 0,75 KW motor and some solinoids
why they charge more bill for low power factor rather than high power factor
What happen if we re-start H.T motor whose rotor is running at 40% rated speed. Is it will damage motor winding?
how can calculate resistance box for 15 kw, 6 pole, RV-230, RA-42 motor
how to find the voltage drop
1 Answers Sharjah Electricity and Water Authority SEWA,
what will happen if a 3 phase motor is connected to a single phase circuit and vice versa?
in elevator industries , how to calculate the required KVA for the elevator (elevator spec- 40A module , motor of 13.5KW, 20A)
1 Answers DLF, Tata Steel Limited,
how to determine Sq.mm size of finolex power cables.
why the neutral point of star connnection oscillates?
give me a clear defination of inductance,and how can u calculate inductance of a motor