Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


I have 200 KVA Isolation Transformer for UPS input side. &
ups was having 48% load, suddenly got short what will be the
reason.



I have 200 KVA Isolation Transformer for UPS input side. & ups was having 48% load, suddenly go..

Answer / m.b.parthasarathy

1. You've not mentioned clearly that the short occurred either in transformer or control board.
2. There my be many reasons.
3. In rush voltage may be higher.
4. The device(IGBT) used in the UPS, would be lower value. say 150A/400/600V
5. for ex, the above said UPS, 200kva/480v dc, due to improper maintenance of battery, weakness or prone to ageing the DC may be very low. Instead of 480V Dc it works only in 444V dc. Two or Three batteries may be getting weak.
6. Insulation of the transformer may be worn out

Is This Answer Correct ?    0 Yes 0 No

Post New Answer

More Electrical Engineering Interview Questions

How can claculate to attain the desired PF in the line ( HOW Much KVAR is required ) Pls Give the formula? Equate Petrochemical 0 1 how to calculate sizing of NGTR (Transformer rating,Loading resistor value and Current rating of resistor) and what is the X/R ratio. Details : 11kV,Capacitance 1.73532 micro farads,40kA for 1sec. 0 1 What will happened. if we feed 3phase supplay to the stater with out insert the rotor. How much current will flow through the stater winnding? Equate Petrochemical 0 1 What is required of exietation to the alternater. 0 1 why star point of HT motor not earthed? Equate Petrochemical 0 1 Why we are getting low voltage in star connection? Equate Petrochemical 0 2 What's ND relay & it's functions? Equate Petrochemical 0 2 How instantanious short circuit current is calculated? its formula? Equate Petrochemical 0 2 What is servo Motor? What's the advantages of this motor over Induction motor? Equate Petrochemical 0 2 What is core CT & it's function? Equate Petrochemical 0 3 what is meant by star/delta voltages as 440/220 in a 3 phase induction motor, and why it should be connected on STAR IN 3 PHASE SUPPLY L & T 0 4 What is required of exietation to the alternater. KNB 1 23 what is the design voltage for 6.6KV 2000 KVAR HT capacitor? Consultancy 0 3 Pls explain about vfd control?Where it is used, Give some example? siemens 1 22 Please explain me abt PQ diagaram in the power sector. 0 9

0 Answers  


how can findout cable fault Location only useing MEGGER

3 Answers  


What is the knee point voltage of CT-100/5,15VA,5P20 ?

3 Answers   ERL, NTPC,


what will happen if the bus PT fuses are accidently removed from the circuit in 6.6kV feeder?

1 Answers  


why transformers are sometimes kept on concrete benches..?

2 Answers  


A 3ph load of 10 KW is equal to how many KW of single phase .

1 Answers  


what is the maximum Load capasity in LV-Panel,MDB,SMDB & Final DB'S in Electrical disribution system?

2 Answers   Sterling,


how to calculate the formula of cable size if motor kw is given

0 Answers   APT,


what is formula in determining the size of Circuit Breaker for transformer with the following specifications. 7 units of 1600 volts (primary) and 400 volts (secondary). Both Primary and Secondary will have a circuit breaker which is SF6. What should be the Switchgear Main Breaker Size anf the sizes of each brances Circuit Breaker for Primary.

1 Answers   ABB,


what is 3rd Harmonics? how it is generated in alternator

2 Answers   Aditya Birla,


Which factor decide the colour of the light emitted from a Led?

3 Answers  


what is the procedure for three phase motor differential relay testing can it do with single phase test kit?

1 Answers   ABB,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)