Hi,,
Just I want ask, if the power factor decrease what happen
in voltage regulation?
Thanks..
due to decrease in power factor, the value of line current
increases.
more line current means more voltage drop (i.e. voltage
regulation), where voltage drop is V=IR.
| Is This Answer Correct ? | 1 Yes | 0 No |
1.stranded resistance values of motors? 2.how to calculate the resistance values of single phase and 3phase motors?
What are the components ofan HT panel in a 11kv power station?
In cable sizing calculation (determining the max route length of cable) why we choose the shortest length between cable length of full load current Iflc & starting current Istart?
Connection diagram for KW meter and Kva meter
before synchronizing an alternator,power factor is leading ,why?
How maesure earth neutral value & how much maximum value value required in between earth & neutral.
What do you mean by pf of a generator? Power factor purely depends on the load (wether inductive, reactive or unity) then what does the pf mentioned on the generator nameplate means?
What is voltage
what is level 2 automation?
Why the electron flow in reverse of current.
in battery charging room we find two fuses (one in positive other in negative cables ).why it is so?one fuse is ore than sufficient?
IF i have switchgear with busbar current rating of 1000Amp 35kA then is it necessary to have outgoing breaker kA rating to be equal to busbar kA rating?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)