Answer / anuj singh
First of all take a multimeter and set in resistance mode and measure if value is near 100 for pt/RTD at room temperature if value is nea zero then RTD is damage.
| Is This Answer Correct ? | 16 Yes | 0 No |
Answer / anuj singh
measure resistance by multimeter of RTD if it is near zero then your RTD damaged.
| Is This Answer Correct ? | 7 Yes | 2 No |
Answer / md gulfraj alam
sorry sir my english is touch week .. first take a multimeter and set in resistance mode and measure the rtd.if 100 ohm resistance at 0° centigrade then rtd pt-100 is ok near value 99-101 ohm resistance.and same case in pt50,pt25,pt500,pt100 etc only value is isolated of all rtd.otherwise rtd is damage when not match the value..i hope u understanding my ans.thank you
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / nvr
it can be known by two different way. first by measuring
resistance by using multimeter and second way to use
measure temp by using temp simulator.
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / rahul singh
PT 100 means, 100 ohm at 0 degree. and 4 ohm increasing
with every 10 degree temp.
eg: if resistance show 120 ohm that means temp should be
show about 50 degree.
| Is This Answer Correct ? | 1 Yes | 1 No |
How to do calibration of magnetic flowmeter
if a dp transmitter has range 100 in H2O and flow is 20mmcf and if the flow is changed to 25 mmcf then what is the formula to determine new range of transmitter
How to Calibrate Ultrasonic flow Transmitter in Field
WHAT IS THE DIFFERENCE B/W PLC and DCS
how to calibrate bubbler type level transmitter of rosemount make and how to set air flow according to the range.. give one calibration procedure with one example
How will you calibrate PID controller? explain with example.
0 Answers Jacobs, Sirte Oil Company,
3. Differentiate between ultrasonic flowmeter and radar type flow meter.
What the basic of communication?
how can loop single 4-20 ma to two isolation amplifier? i mean i have two isolation amplifier with 4-20 ma input and 1-5 v output.can i done series connection ?
What is the difference between HMI and SCADA?
how to calibrate transmitter
What is the working principle of Dozing valve used in cement industry?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)