what is the voltage regulation constant of ACSR Raccoon
conductor
Thus for33kV line with 48 sq mm ACSR conductor, the maximum
limit is135 MW-KM at 9%
voltage regulation and 0.8 PF.
For 11KV and L.T. lines, the maximum kW-km at permissible
Voltage Regulation are tabulated below
However, some State Electricity Boards follow regulation limit
as 5% and 8% respectively. The
load carrying capability of 33 kV and 11 kV lines is given
below:
For 33kv Raccoon the permissible voltage drop is 5%.
Is This Answer Correct ? | 11 Yes | 8 No |