what is the voltage regulation constant of ACSR Raccoon
conductor
Thus for33kV line with 48 sq mm ACSR conductor, the maximum
limit is135 MW-KM at 9%
voltage regulation and 0.8 PF.
For 11KV and L.T. lines, the maximum kW-km at permissible
Voltage Regulation are tabulated below
However, some State Electricity Boards follow regulation limit
as 5% and 8% respectively. The
load carrying capability of 33 kV and 11 kV lines is given
below:
For 33kv Raccoon the permissible voltage drop is 5%.
| Is This Answer Correct ? | 11 Yes | 8 No |
what is the relationship between induction motor and transformers?
11 Answers College School Exams Tests, Engineering, Reliance,
why do power factor in the three phase induction motor increases with the load ???.
why do we need a 4th wire in 3phase 3wire transmission line
what is the gas pressure at normal & operating conditions of sf6 cb??
how to measure dc earth leakage current?
what's the reson that,Load is not same on VFD I/P and O/P Side.whenever DOL condition load is same I/P and O/P side.
what is corona ?
ther is any difference if we use 240 V A.C,50 Hz,1 Ph. in place of 230 V A.C,50 Hz,1 Ph.
please mention the minimum IR value for different voltage systems
The capacitive reactance of a capacitor of 1/(2(PI)) F at 10^3 H is
What are the types of excitation system?
How can calculate the daily electrical consumption of 7.5 HP motor, if the moter runs 24 hrs continiously. Also have to know about 3.5 hp chiller.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)