Answer / yoyoma
These are the steps required to detemining the cable size
required for your motor.
1) Determine the FLA (full load amps) or FLC (full load
current) of the motor. This can be obtained from the
motor nameplate or datasheet. If these are not avaiable
refer to the charts in the NEC or CSA code books.
2) As per NEC and CSA the cable is to be sized a minimum of
an additional 25% of the rated FLA or FLC (FLAx1.25)
3) Next a derating factor may need to be applied for both
temperature and grouping of cable in a raceway or cable
tray. These should be found in your code books. Multiply
these factors to your answer from number 2 above.
4) Once you have done 1 through 3, you should have a
current value larger than that of the rated FLA or FLC
of the motor. Use this current value to select the cable
size that can handle this current.
5) Lastly, as a verification you must also determine if the
cable size selected in number 4 above is sized so that
the voltage drop is no less than 3% (some go as high as
5%) of the source voltage (in your case 4400V x 0.97 =
426.8V). If your cable is undersized then you must
continue to increase the size until the voltage drop is
within 3%.
6) Once these are all done, your cable will be sized
correctly and accounting for all additional factors.
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / wareagle
1. Determine the amperage for the 10 hp motor. You can do
this by looking at the NEC chart at this site.
http://www.electricmotorshop.net/index.php?
option=com_content&view=article&id=687&Itemid=352
2.From this chart the 10 HP requires 14 amps. You then go
to a wiring table and select the conductor that has an
ampacity of 14 amps or more. The local code will dictate
your selection.
3.This wire choice does not include voltage drop
requirements.You may need a large size to reduce voltage if
necessary.
4. local codes may dictate other requirements.
| Is This Answer Correct ? | 5 Yes | 3 No |
Answer / r k choudhary
first we have to find out the ampere then as per cable
sizing chart select the cable but one thing always kept in
mind that for safe working (losses ,voltage drop,efficiency
of motor) consider somthing extra size of cable.
| Is This Answer Correct ? | 1 Yes | 1 No |
Answer / sudhakar
depending on the current rating of the motor only we will
choose the cable rating and consider the current density of
the copper also important
| Is This Answer Correct ? | 2 Yes | 3 No |
What is given by the definition in BIL IMP/PF = 950/395 kV. This was found in a name plate of a power transformer.
how can motor both beasrings insulation resistance can be check?
What are the role of each components in PID COntroller
What is the difference between earthed and unearthed cable
what is exiter winding,stator winding,avr?how it will work?
How many types of losses occur in a transformer?
What is Hi-Pot Test for Grid Station HV Equipments?
ward lconard control
Why a Permanent Magnet Generator has higher frequency as compared to frequency of main alternator?
How to calculate the no of Ceiling fan (1200mm sweep) per unit area?
practicalLY what is impedence ...?
We've 2 diffrent DG's with same capacity (500 KVA). Can we sync them ?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)