Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


for selection of transformer we will considering 5 to 6
times of starting current of higher rating motor connected
to secondary side. according to process wise we will start
the motors gradually suppose if we will start 15 to 20
motors at a time wat will happen?



for selection of transformer we will considering 5 to 6 times of starting current of higher rating..

Answer / wareagle

If you start all of the motors at the same time then you
will have the sum of the lock rotor amps time the number of
motors occurring at the same time. You may trip the primary
transformer breaker.

Is This Answer Correct ?    4 Yes 0 No

Post New Answer

More Electrical Engineering Interview Questions

what is suitable cable for 25 HP motor ? start with VFD ac supply 50 hz

3 Answers   Mac,


Why glands not provided for XLPE cables

1 Answers   Saint Gobain,


what is the transformer turn ratio formula and give some examples?

0 Answers   UPPCL,


What is the difference between shortcircuit current, rated current of cable & MCB with example? What will be the size of cable required for 5.5 KW motor (Full load current 10 Amps approx.), Starting current with DOL is 120 Amps. Aprrox. Short circuit current with LLLG fault is 2000 Amps Approx.

0 Answers  


what is the difference between contactors & relay.

2 Answers  


To determine the Healthiness of Insulation we will be performing Dielectric tests i.e Insulation Resistance test, Partial Discharge test,Switching Impulse, Lightning impulse, Tan Delta test ...etc why we required to perform this many test, why cant we do only one test. for Transformer, CT's

1 Answers  


Why Powers are named in MW?

1 Answers  


How to calculate cable size by using load.?? Any formula...

0 Answers  


Should power factor be low or high?

0 Answers  


what is role of mpu in dg

1 Answers  


what happen to a dc series motor if it given as ac supply accidentaly

2 Answers   ONGC,


why we use REF and Differential Protection in one transformers?my doubt is both protections are operated in internal fault only.why we want to use 2 protections?please clarify.

7 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)