why open circuit test is conducted on hv side and short
circuit test is conducted on lv side of a transformer ?what is
the reason for it ?
Answers were Sorted based on User's Feedback
Answer / c.tharakeswara reddy
In open circuit test HV is open, LV is connected to supply
meters also connect to lv side why because availabilty of
high range voltmeters is not easy(hv voltmeters are
costly),conductnig test on lv or hv we get same result.so
why need to conduct on lv side and make experiment costlier.
In short circuit test LV is short circiuted HV is connected
to supply,meters also connected to hv side. sc test is
conducted on rated current.HV side current is low so we can
use low range ammeters.conductig test on lv or hv we get
same result.if we condct test on hv we need high rage
ammeters. it makes experiment costlier.
| Is This Answer Correct ? | 156 Yes | 66 No |
Answer / nitish prajapati
short ckt test is performed at rated current,as the rated current on hv side is much less than lv side so the rated current is easily achieved(compared to lv side).
| Is This Answer Correct ? | 59 Yes | 6 No |
Answer / imtiyaz rasool
short circuit test is conducted on LV side because the voltage on LV side is low compared to HV side so their is less chance of getting shock from low voltage on LV side
| Is This Answer Correct ? | 5 Yes | 40 No |
What is meaning of Float Charging of Batteries???
How much allowable difference current between on three phases Dear sir, We have a 1870 KW HT motor, 11 Kv supply,FLA-120A,2870 rpm,2-pole squirrel cage induction Motor.And stator is connected in star connection with Liquid resistance stater to limit the starting current.It has coupled with Centrifugal air compressor.My question is it is loading 73% of FLA taking R-phase 86.7 A, Y-phase-85.4A,B-phase- 78.3A.why the B phase current is that much of difference.Is it allowable, or any one tell me how much allowable current.If any method to calculate.
How to calculate the size of earth cable to earth the neutral of UPS ?
what are the main problems that happen in an emergency light and how to fix them ?
whether choke act as a voltage regulator in tubelight or not?
what is load cell? whrere its used ? how to measured?
If connected load of Asphalt plant is 375Kw. What suitable KVA DG set is required. What is calculation formula. what extra load have to consider. in what efficiency it will work.
Give me clear explanation.What is the Different Between Load break switch and Vacuum circuit breaker
HOW DEFINE THE IP FOR ELECTRICAL EQUIPMENT AND WHAT IS THE IP OF PANELS USING IN HAZARDOUS AREA ?
why magnetising curve not start with zero voltage?
Between Turbo alternator and Hydro alternator which one is more difficult to cool and why?
How would your past experience translate into success in this job?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)