why open circuit test is conducted on hv side and short
circuit test is conducted on lv side of a transformer ?what is
the reason for it ?
Answers were Sorted based on User's Feedback
Answer / c.tharakeswara reddy
In open circuit test HV is open, LV is connected to supply
meters also connect to lv side why because availabilty of
high range voltmeters is not easy(hv voltmeters are
costly),conductnig test on lv or hv we get same result.so
why need to conduct on lv side and make experiment costlier.
In short circuit test LV is short circiuted HV is connected
to supply,meters also connected to hv side. sc test is
conducted on rated current.HV side current is low so we can
use low range ammeters.conductig test on lv or hv we get
same result.if we condct test on hv we need high rage
ammeters. it makes experiment costlier.
| Is This Answer Correct ? | 156 Yes | 66 No |
Answer / nitish prajapati
short ckt test is performed at rated current,as the rated current on hv side is much less than lv side so the rated current is easily achieved(compared to lv side).
| Is This Answer Correct ? | 59 Yes | 6 No |
Answer / imtiyaz rasool
short circuit test is conducted on LV side because the voltage on LV side is low compared to HV side so their is less chance of getting shock from low voltage on LV side
| Is This Answer Correct ? | 5 Yes | 40 No |
EXPLAIN METOD OF IMAGE OF TRANSMISSION LINE/ WHAT ARE ITS PRACTICAL APPLICATION?
what is the difference between synchronous & asynchronous generators
size of condotory fron voltage level
what is the minimum clearance between a 11KV 150KVAR capacitor cell and series reactor.can a series reactor can be mounted in the same structure of the capacitor cells structure
What are locations arc protection relay is fixed.
How many different speeds can be obtained in cascade control of two induction motors?
WE are using a 63A MCCB(SIEMENS MAKE) for one of the feeder in LV substation panel.It is supplying to a lighting & power socket DB.Settings in the MCCB is Ir = 63 * 1 , Isd = 8 times of Ir , tsd = 0.5 sec( I2 t off). Sometimes this MCCB is tripping .But no trip in DB MCB. Can anybody tell me reason ? From where i can know about the MCCB settings?
why buchholz relay installed in inclined position
What is slip in an induction motor?
a distribution transformer(3 phase)supplying 440volt per phase.now suppose one of phase voltage(230volt) becomes zero.what will be the cause ?
installation of subsatation of33kv
what is the difference between on line & off line UPS
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)