what happen if i install my pressure transmitter below the elevation of pipe in natural gas service. Also support your answer
Answers were Sorted based on User's Feedback
Pressure will be added up a bit more, see its detail:
1. Suppose,you want to install a pressure transmitter 10
meter below of pipe line.
2. Density of methane (Examlpe) 0.656 kg/m3 at 25C.
3. your pressure transmitter will show (10 x 1000 x0.656 =
6560mm) 6569 mm of water pressure more.
4. Suppose gas pressure is 20Kg/cm2, then due to this
elevation, transmitter will show 20.66Kg/cm2
aftabmazari@yahoo.com
Is This Answer Correct ? | 6 Yes | 1 No |
Answer / narayan
it will not give correct pressure, since natural gas condense in the lower side, actual pressure will be added with this head pressure of liquid, hence it will not give the actual pressure of gas
so transmitter should be installed above the pipe line, to measure exact pressure of NG
Is This Answer Correct ? | 3 Yes | 0 No |
how we can calibrate an Interface level transmitter online
What is the definition of direct acting valve & reverse acting valve
-/5A. What is the meaning and limitations of this in energy meter constant. It is a 3 phase LT Energy Meter. If this Energy Meter is connected through a CT of ratio 200/5 Amps, then what is the multiplying constant and how its will be calculated.
What is the standard height for stancion supports?
Can combine control system for Emergency control system (ESD)and Fire & Gas System ( F & G) is possble to built and offer to client? Can such system is as per Norms in India?
What are different types of cable?
In RTU Panel we are having several Analogue & Digital Inputs /Outputs. We are recently facing some problems over Analog inputs , which are not updating properly (But Digital Input are updating normally) Can any one tell me from where the problem is creating , we have checked PLC CPU card, Analog Input card & we reconfigured ,But still the issue is there. Issue : 1. Sometimes Analog values are updating & sometimes not. 2. Analog values are not updating normally , showing some wrong Values 3. Total dead (0 value) Analog values are Level & flow measurement from the field instruments. (But in field the instruments are working normally & Displaying the values normally in local display unit) This problem we are facing in our Water Plant. If any one experienced this same problem or having any ideas related to our issue PLS send your valuable Answers/Replies...
What is the solution if rotork motorised control valve showing pink Colour in dcs.
3 Answers Bhushan Power Steel,
1.In which princeple DP transmeter works? 2.Why UPS system is use for DCS? 3.How drum lvel controller works? 4.What is the difference between glob valve and gate valve? 5.How axial shift probe work & in which princeple it works?
1 Answers Luberef, Qatar Gas, Reliance,
why the output sugnal is 4-20 ma and not 4-25 ma?
plz send me general of ongc
NAME ANY TWO PHOTO CONDUTIVE MATERIALS?