for commissioning the DPT and Flow Transmitter , what kind
of necessary activities we have to check and do?
specially that orifice flange valve[ isolation valve}
Answer / carl_ellis
Here's Mr. Emerson's view on loop checking with instructions
for zero checking a DP transmitter on a 3 valve manifold:
Wiring Checkout and Loop Check
The first step in commissioning a new instrument is the
physical installation. The physical installation steps are
the same for both the traditional and new approach:
1. Review P&ID drawings for location and piping instructions.
2. Review device instructions for proper location, mounting,
and piping.
3. Verify field device is physically located in the correct
location per the P&ID. Verify that a permanent tag label is
securely attached to the device that clearly indicates the
assigned loop tag number.
4. Verify field device is correctly connected by performing
the following inspections:
a. Physical inspection- properly mounted and oriented as
designed, ensure close-coupled connections are securely
fastened; pipe stands are structurally sound
b1. Mechanical - Sensing lines, and other process
connections are properly installed, connected and verified
per instrument design specification
b2. For DP transmitters with manifold valves:
- Always perform a zero trim on the transmitter/manifold
assembly after installation to eliminate
any shift due to mounting effects.
- In normal operation the two block valves between the
process and instrument ports will be open and the equalizing
valve will be closed.
- To zero the DP transmitter (3 valve manifold), close
the block valve to the low pressure (downstream) side of the
transmitter first.
- Open the center (equalize) valve to equalize the
pressure on both sides of the transmitter. The manifold
valves are now in the proper configuration for zeroing the
transmitter.
- After zeroing the transmitter, close the equalizing valve.
- Open the block valve on the low pressure side of the
transmitter to return the transmitter to service.
c. Electrical - Conduit runs are properly connected; seal
drains are installed correctly, etc.
5. Verify the input or output signal is within the device's
normal operating range.
6. Verify that any special/custom device characteristics
required are present (example: custom gas curves, special
construction materials, etc.)
7. Measure and adjust associated air and electrical power
supplies.
8. Measure loop impedance by disconnecting the signal wiring
at both the transmitter and rack room ends, shorting the
signal wiring at the transmitter and measuring the loop
resistance with an ohmmeter at the termination panel end.
This process typically takes two technicians with two-way
radios for communication.
9. With an ohmmeter, verify there are no shorts to ground in
the signal wiring by checking the wiring to ground while the
wiring is still disconnected. This process typically takes
two technicians with two-way radios for communication.
10. Verify proper wiring polarity.
11. Connect the wiring to the transmitter in the field and
in the rack room.
12. Verify that all field wiring is properly labeled per the
instrument loop diagram. This includes
all terminations per the instrument loop diagram.
13. Verification that all instrumentation wiring is
mechanically sound by performing a physical "Tug Test" of
the wires.
14. Verify that the field device enclosure is closed, all
temporary shipping stops removed, and the device is
mechanically fit for service as defined above and in the
device instruction manual.
15. Apply power to device.
| Is This Answer Correct ? | 1 Yes | 0 No |
WHAT IS MEANT BY PROJECT MANAGEMENT STRATEGIES IN INSTRUMENTATION?
why cant we use mV instead of mA?
12 Answers ABB, Power Grid, Qatar Gas, USW, Visa Steel,
How a rtd work, and what volts/current goes to a RTD to measure the resistence?
Instrumentation engineer please reply me,I am electrical engineer ,what is the future in instrumentation dept {presently working (P&ID) Design} for me,whether good future for me as instrumentation department.what side can i get job in future
What is surge and how is it prevented.
can we copy the software from a transmitter using hht(hart 275) ?
how the 2.5bar pressure able to control the 40bar steam
8 Answers IBM, PAFL, Thirumalai Chemicals,
What is pipe schedule? What are all effects its having in the valve? how do we take care of pipe sch in case if the customer dint specify in the data sheet. What we need assume and in what basis?
can anybody tel me how a vfd or any field instrument communicates/interface with plc/scada/cs.
how to calibrate electro pneumatic positioner 8013 mil controls ltd ?gsr
What is Span Error
hello this is dhinakar i am completed my instrumentation engg . recently i got job in sugar industry side. i like to ask one question can any one say what are the things i have to follow know more about industrial instrumentation,,,,,,,
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)