SUPPOSE A CIRCUIT BREAKER HAS TRIPPED THE THE LINE WHEN A
FAULT OCCUR ON IT.NOW WHEN THE FAULT HAS BEEN CLEARED, HOW
THE CIRCUIT BREAKER WILL CLOSE AUTOMATICALLY NOT MANUALLY.
Answers were Sorted based on User's Feedback
Answer / tanmay kumar
No,we have to make it manually by reseting the operated relay.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / jaydeep
FIRST OF ALL SWITCHGEAR ARE CONECTED AND THAN AFTER C.B.
ARE CONNECTED B'Z SWITCHGEAR ARE USED TO DISCONNECT OR
RECONNECTION OF THE SYSTEM FROM LIVE ENERGIES .
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / yusuf
Once the Fault Cleared the CB Can be closed automatically
using Auto Re closure Relays... Auto reclosing relays are
available on different brands like SIEMENS, ABB and etc.,
| Is This Answer Correct ? | 2 Yes | 2 No |
Answer / gavin
Circuit breaker miniture as found in a consumer unit or
air as in a switch panel. MCB will not auto reclose as per
BS7671.
ACB will auto reclose using shunt coil but not if earth
fault is not reset first manually
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / mg
There is autoreclose function in protection relay(autoreclose relays) if fault is cleared the relay give close command to CKT breaker.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / iqbal.aizza
with the help of springs which are placed both sides of
contacts.
| Is This Answer Correct ? | 2 Yes | 3 No |
how will calculate the safe starting current of 3-phase squirrel cage induction motor?
Where is 2 phase supply used commercially?
For 300 MW plant what is the distribution voltage
If we have 630kva step down transformer to operation 3 phase motor 150 kva which size of cable is used? at circuit breaker to 3 phase motor or to electrical board
I have carried out wiring for lighting in a shed in Industrial area which contains Metal halide lamps & have balanced in 3ph.Now when we put all the lines on in the daytime the current taken at 3phases at MCB comes to be equal i.e.28,29,28Amps respectively but in the night time i.e between 7p.m.to 11p.m. at the same MCb the current is 52,59,62Amp, though I have fit 63A MCB it is tripping in the above period.What may be the reason.? Note: This industry is located in industrial area where majority of steel ingot manufacturing plants are there. Whether this may be due to harmonic? what should I do to overcome above problem.pl suggest urgently.
Why we are use 11KV / 22KV / 33KV / 66KV / 110KV / 230KV / 440KV this type of ratio. why cant we use other voltage ratio like 54KV / 99KV et.,
8 Answers College School Exams Tests, Hino, ITC Infotech, Reliance, UPRVUNL,
How one may guess the direction from which the distribution line is incoming if there is no pole plate on poles?
as per BIS supply voltage in India is ......
Why PT is fitted in incomer panel.....?
why a motor rating in KW?
is emf is indued if dc is passed through coil
any one guide me to reduce the power factor of diesel Generator from 0.97 Leg to 0.8 Leg.with out any change in my load.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)