why are the likely reasons for bochholz & pressure relays
oprate due to a internal fault but not differential relay ?
Answers were Sorted based on User's Feedback
Answer / yusuf
Buchholz and Pressure relays such as Over Surge Relays are
also known as Gas operated relays... Consider an internal
fault such as inturturn fault in the transformer winding,
then the oil temperature raises which in turn produces Gas
inside the Oil Tank.. This Gas passes through the pipe
connected between Oil Tank and Conservator Tank and relay is
placed in the pipe work... so the Gas passes through the
relay and gives an alarm first and then trips the
transformer when the fault is severe.... Differential
protection is based on the principle of Differential current
which compares the current at the two sides ( LV & HV )of
the Trafo... And that's the reason the Differential
protection does not operate for incipient (Slow developing)
Faults
| Is This Answer Correct ? | 9 Yes | 0 No |
Answer / s.panneer selvam
I agree with the answer but i found that the differential relay is high impedance relay, in which we cannot used differential relay for transformer internal fault. Because due to mismatch in CT's and lead connection ur circuit will trip spuriously even if there is no abnormality when CT are requested for 100% protection. so we compelled to use some stabilizing resistor which creates non operative zone for some part of winding.where a incipient faults are not continous fault which exists in circuit , it is discontinuous fault after some it may not be in circuit.
| Is This Answer Correct ? | 0 Yes | 0 No |
what is load which is indicated in power plant generation panel? in any power plant
HOW TO DRAW THE VECTOR DIAGRAMS OF A Dyn 11,YdN 1 transformers?
I have connected 04nos. earthings to a transformer through 04nos. earthing pits seperately. 02nos. earthings are connected to T/F body, and 02nos. earthings are connected to T/F neutral.T/F capacity is 2000KVA, 11KV/415V. But after completing of 02 years successful operation ,we are facing following problems- 1. CT/PT occured blast one time 2. HT cable box occured blast two times 3. One body earthing strip and one neutral earthing strip of transformer are overlapping at some places. Whenever these two strips are pressed at overlapped points, they made spark. What is the reason of spark? Please explain the reason & rectification of above problems
what is a kit kat fuse?
why colour of electrical equipment( like transformer) is grey
i have install 750 kva distribution transformer at my site and want to do neutral earthing. what calculations should i follow to determine earthing conductor material and size?
How to calculate Grid rotor resistance(GRR) losses in slip ring induction motor?
what is different between phase and netural
WHAT IS PRINCIPLE OF TRANSFORMER
2. What are the parameters of EHT sub-station?
1 Answers APGenco, Blue Star, Enercon,
What is resolver and glass scale in CNC how they work?
what is the current generated in a 230v megger?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)