Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


why are the likely reasons for bochholz & pressure relays
oprate due to a internal fault but not differential relay ?

Answers were Sorted based on User's Feedback



why are the likely reasons for bochholz & pressure relays oprate due to a internal fault but no..

Answer / yusuf

Buchholz and Pressure relays such as Over Surge Relays are
also known as Gas operated relays... Consider an internal
fault such as inturturn fault in the transformer winding,
then the oil temperature raises which in turn produces Gas
inside the Oil Tank.. This Gas passes through the pipe
connected between Oil Tank and Conservator Tank and relay is
placed in the pipe work... so the Gas passes through the
relay and gives an alarm first and then trips the
transformer when the fault is severe.... Differential
protection is based on the principle of Differential current
which compares the current at the two sides ( LV & HV )of
the Trafo... And that's the reason the Differential
protection does not operate for incipient (Slow developing)
Faults

Is This Answer Correct ?    9 Yes 0 No

why are the likely reasons for bochholz & pressure relays oprate due to a internal fault but no..

Answer / s.panneer selvam

I agree with the answer but i found that the differential relay is high impedance relay, in which we cannot used differential relay for transformer internal fault. Because due to mismatch in CT's and lead connection ur circuit will trip spuriously even if there is no abnormality when CT are requested for 100% protection. so we compelled to use some stabilizing resistor which creates non operative zone for some part of winding.where a incipient faults are not continous fault which exists in circuit , it is discontinuous fault after some it may not be in circuit. 

Is This Answer Correct ?    0 Yes 0 No

Post New Answer

More Electrical Engineering Interview Questions

what is the difference between the 94 lockout relay and 86 lock out relay. I have noticed that the 94 lockout relay is activated when the distance realy is activated and 86 is activated when the 87T differential is activated. but why can't the same lockouts be used for both the protection schemes

10 Answers   ABB,


what is meant by excitation which supply is used whether ac r dc in the lab applications

1 Answers  


What are the different condition monitoring techniques for a motor?

1 Answers   DAE,


What is a advantage of Self Reset Lockout ? On Fault breaker get trip & fault no longer exist then self reset lockout how inform us?

0 Answers   Bhad Engineers,


The Q-facr o of a coil given as wL/R. what will be shape of Q versus frequency graph.

0 Answers   GATE,


how we select HRC FUSE ?

1 Answers   AXA,


What is excitation in case of dc motor?

0 Answers  


We store the d.c supply...then why can't we store A.c supply???

4 Answers  


why we use 50 hz frequency in india .. why not 60 hz 

3 Answers  


how synchronous generator can be used as synchronous condenser?

3 Answers   Monnet, Wipro,


What happened If 3phase supply connected to slip ring side of slipring induction motor ?

2 Answers  


how the length effects the ampacity of the cable? if a cable is carrying a current of 100A for 50m length then what will the effect on current if we double the length?

2 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4453)
  • Electrical Engineering Interview Questions Electrical Engineering (16638)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)