Answer / r.murugan

o2 analyzer need zero and span gas for calibration

zero gas will be standard parameter

span gas will be standard parameter

you have to select calibration mode

if select zero gas calibration (cyclinder open) enter while
zero gas calibration finish it should reach actual standard
gas value if reached close the zero gas cyclinder

we can proceed to span gas calibration open the span gas
cyclinder select the span gas calibration enter while span
gas calibration finish it should reach standard span gas
value if reached we close the span gas cyclider

Is This Answer Correct ?    6 Yes 3 No

what is the procedure of O2 analyser calibration?..

Answer / mahesh

O2 analyzer input connection removed and checked in atmosphere oxygen percentages after setting o2 sensor 20.1% in o2

Is This Answer Correct ?    1 Yes 0 No

what is the procedure of O2 analyser calibration?..

Answer / macchindra

In atmosphere the O2 content must be 20.8%

Is This Answer Correct ?    0 Yes 1 No

Post New Answer

More Instrumentation Interview Questions

How can SmartPlant Instrumentation users take advantage of these global services?

1 Answers  


Describe the concept of Gain Scheduling, as currently found as an option in some controllers.

1 Answers  


Which topics are covered in Process Control?

0 Answers   Honeywell, L&T,


What is the PLC configuration in Cement industry?

0 Answers   IMCO, Maha Cement,


why would you like to join our company

0 Answers   Aramco,






what is the difference between Ethernet unmanaged and managed Switch?

2 Answers  


Example of dry contacts & wet contacts?

3 Answers  


What is Hysteresis mean in Instrument?

11 Answers  


What is the cv of a control valve?

2 Answers   CCIE,


what is temperature compensation?

1 Answers  


A temperature sensor (RTD) connected via a temperature transmitter is adjusted to give an output of 4ma at 60 deg and 20 ma at 600 deg. This output (4-20ma) from the transmitter is connected to an IGBT-inverter to control a high speed (-12,000 to +12,000 RPM) DC motor. And in the inverter it is programmed as, for 4ma the motor speed will be -3,000 RPM and for 20ma the motor speed will be +10,000 RPM. The question is : If the motor speed is +5,500 (RPM), what will be the temperature? (-sign indicates that the motion is in reverse direction).

9 Answers  


Why do we go for 4-20mA? why not other standara?

6 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)