Answer / r.murugan
o2 analyzer need zero and span gas for calibration
zero gas will be standard parameter
span gas will be standard parameter
you have to select calibration mode
if select zero gas calibration (cyclinder open) enter while
zero gas calibration finish it should reach actual standard
gas value if reached close the zero gas cyclinder
we can proceed to span gas calibration open the span gas
cyclinder select the span gas calibration enter while span
gas calibration finish it should reach standard span gas
value if reached we close the span gas cyclider
Is This Answer Correct ? | 6 Yes | 3 No |
Answer / mahesh
O2 analyzer input connection removed and checked in atmosphere oxygen percentages after setting o2 sensor 20.1% in o2
Is This Answer Correct ? | 1 Yes | 0 No |
How can SmartPlant Instrumentation users take advantage of these global services?
Describe the concept of Gain Scheduling, as currently found as an option in some controllers.
Which topics are covered in Process Control?
What is the PLC configuration in Cement industry?
why would you like to join our company
what is the difference between Ethernet unmanaged and managed Switch?
Example of dry contacts & wet contacts?
What is Hysteresis mean in Instrument?
What is the cv of a control valve?
what is temperature compensation?
A temperature sensor (RTD) connected via a temperature transmitter is adjusted to give an output of 4ma at 60 deg and 20 ma at 600 deg. This output (4-20ma) from the transmitter is connected to an IGBT-inverter to control a high speed (-12,000 to +12,000 RPM) DC motor. And in the inverter it is programmed as, for 4ma the motor speed will be -3,000 RPM and for 20ma the motor speed will be +10,000 RPM. The question is : If the motor speed is +5,500 (RPM), what will be the temperature? (-sign indicates that the motion is in reverse direction).
Why do we go for 4-20mA? why not other standara?