what is three element in thermal boiler
Answers were Sorted based on User's Feedback
Answer / nirmal
THE THREE ELEMENT IN BOILER IS STEAM FLOW,FEEDWATER FLOW
AND DRUM LEVEL.
| Is This Answer Correct ? | 15 Yes | 0 No |
Answer / varun kumar
It maintain the drum level with the help of making balance between feed water and steam flow.
| Is This Answer Correct ? | 4 Yes | 1 No |
Answer / nileshkumar jambukiya
THE THREE ELEMENT IN BOILER IS
(1)STEAM FLOW
(2)FEEDWATER FLOW
(3) DRUM LEVEL
we use multiloop controller with cascade facility to
control drume level, in this level is use as a primary
setpoint SP, the out put of primary loop is being setpoint
of secondary loop and this is water flow, so that if our
primery setpont is maintain automaticaly steam pressure
maintain. so we use three element in boiler drume level.
Thanks,
JAMBUKIYA N.T
| Is This Answer Correct ? | 2 Yes | 2 No |
Answer / nivrutti gavali
These are three parameters which are required to control in
order to ensure the healthiness of boiler.
1: boiler feed water flow control
2: boiler fuel firing control
3: boiler drum level control
| Is This Answer Correct ? | 3 Yes | 6 No |
Answer / mukesh budhauliya
These are three parameters which are required to control in
order to ensure the healthiness of boiler.
1: boiler feed water flow control
2: boiler fuel firing control
3: boiler drum level control
| Is This Answer Correct ? | 2 Yes | 9 No |
Answer / bhabani shankar dash
This is generally calculating inside logic by taking analog
value's from Total Air Flow + Drum Level(A or B or C) + Feed
Water Flow.
| Is This Answer Correct ? | 3 Yes | 16 No |
How will you test a transistor with a multimeter?
why we cant transmit the dc current easily
what is the formula for calculating milliampere at different pressure points for eg 4-20 ma = 3-15 psi but if i have to check the ma at 4.6 ma?
can you send remote seal interface level transmitter calculation steps for oil water saperator.
0 Answers Sasol Firm, Thermax,
can we use a control valve without positioner
Boiler flame scanner working principle?
how works encoder in plc
In split range control, we will control 2 outputs with time interval. Eg :(with 4-20 ma signal, for 4-12 ma we are operating one control instrument like valve & for 12-20ma we are operating other control instrumet (other valve). If we get a signal of 15ma to first instrument (Valve 1), what will happened to the first valve, and if we get signal above 20 ma to 2 valve what will happened ?
what is the square root flow transmitter formulla ?
What is PLC(programmable logic control)?
In Increasing temperature why thermocouple used and RTD is not used. Both RTD and Thermocouple have in Range of uses.
how to set calibration range in a DP transmitter to measure level for a closed tank and for an open tank,and also please explain me how to set calibration range for a DP flow transmitter in a line ?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)