1)how we calculate the drum level? and how we select the
transmitter range?
Answers were Sorted based on User's Feedback
Answer / jsindrajit
Drum level is measured by measuring the differential
pressure accross two tapings(Bottom & Top)in the drum by
using DP transmitter, whose HP side is connected with the
Taping coming from the bottom and LP side connected with
the taping coming from top.
HP side will have a pressure of Both the Steam Pressure and
Water Level. At the same time LP side will have only Steam
Pressure. Therefore the transmitter will reflect only the
Water level.
The range selection for transmitter depends mainly on three
factors i.e. Drum working Temperature, Drum working
Pressure and Difference of pressure between two tapings.
There are other factors also like Dade band, accuracy,
repeatability, response time etc.
| Is This Answer Correct ? | 5 Yes | 2 No |
Answer / ram
First of all u should be clear about which kind of liquid
level u want to measure? B'coz selection of level
transmitter depend on it. So many x'mitter are available
with different types and range according to the application.
And range is depends on ur drum size.
| Is This Answer Correct ? | 3 Yes | 3 No |
Answer / george mathews
if we are trying to measure the drum level of a drum which
contain water or (H2O) we prefer to use the Hydrastep .
Which is in my knowledge one of the trusted sencer of it
kind .
Anather by using the pressure or more preciesely the DP
transmitter. Here what we do is , we take the connection of
the higher end of the DP Transmitter from d bottm of the
drum and simulteneously we take the connection form the
upper end .where we can find the difference and calculate
the level of water it has got. as during the time of
calibration it is being feeded what ll b d pressure of the
drum when it is full and what is the pressure when it is
empty .
so it ll differenciate the difference between the actual
lever of water level of the drum.
Here the key factor is the density of Any medium , once we
know the Exact density of the Medium we can find the level
easely with the DP Transmitter.
| Is This Answer Correct ? | 0 Yes | 0 No |
How to Calibrate the magnetic flow meter on site ?
What is the loop calibration? Which instrument used to loop calibration and how?
What is the use of GMV in turbine?
0 Answers Hamsco, Maruti Suzuki,
WHAT IS THE MASS FLOW FLOW METER
hi! i want to know about mpse exam.
When doing a liquid seal on a differential flow transmitter , most of the time the sealing liquid will be heavier then the process fluid. For wich application will the sealing liquid be lighter than the process fluid if transmitter is mounted below the process line.
Which types of quections asked in interview for FORMULATION PLANT (PHARMA)
Yokogawa CENTUMVP R6.09 unable to download to Engineering Station with ExaOPC R3.75 The issue is when I try to download the common project section to the Engineering Station (STN) from the HIS in System View, it is unable to connect. The error displayed is: WARNING: Could not connect to equalize destination. (7001) Retrying. Number of retries = 0/1 ERROR: LdXopsLoadMain: connect error 10060 ERROR: Processing terminated due to connection error. (7002) Equalization end with errors. STN0149 ---- ERROR = 2 WARNING = 1 ---- Background: >Updated the ExaOPC software on the STN from 3.60 to 3.75 >STN operating system is Windows Server 2008 R2 >HIS operating system is Windows Server 2016 Stanard Solutions attempted include: >Ensuring all IP addresses are correct and all networked devices can be pinged. >The ability to ping a device using its host name from another device (<ping STN0149> from HIS) >Ensure both devices firewalls are disabled. >The antivirus installed on the STN is disabled. >Ensuring both devices are within the same workgroup. >Added both devices to each other's Host and LMHost files. >Running IT Security tool after changing any administrative settings.
why we should maintain neutral earth voltage below 1V while calibration? why cant it be 1.2V or 2V
how to calibrate the temprature transmitter MURCREYtype and thermocouple input type.
how can we measure the pressure in underground cooling water pipeline by using pressure transmitter?what about the tapping position?
what is the function of a zener diode ?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)