Answer / vishal ingle
the CT works on the principle of
Primary AT = Secondary AT
When current is flowing through primary, there must be
path for the secondary current to flow.
Else heavy ovevoltage will be induced in the secondary
winding which is sufficient for insulation failure and
busrcting of CT.
Hence CT secondary should always be short circuited
Is This Answer Correct ? | 5 Yes | 3 No |
Answer / k
The output voltage will rise trying to develop current until
it reaches the saturation voltage of the coil at that
frequency. At that point, the voltage will cease to rise and
the transformer will add no additional impedance to the
driving current. Therefore,the output voltage of a current
transformer will be its saturation voltage at the operating
frequency.
Is This Answer Correct ? | 0 Yes | 1 No |
why single CT used in DOL starter power circuit?
how many types of Earth bits available
how calculate the electrical load for industry and office
How neutral voltage for transformer decided? eg 33kv neutral voltage for 200MVA transformer?
we know the value of the power factor is 0.8, we know the power factor is not depends upon the load ,then why we cant design the power factor in transformer ?
why tertiary winding is used in transformer with diagram?
What is the difference between type1 and type2 relay protection co-ordination for motor feeders
WhY PF low at Time of PT Missing in HT Meter
What is time invariant system?
why in some trains in India Electric equipment such as Fans , tube light not work until locomotive or engine is attached to the train ??
What is working principle of ACB and VCB?
how to select a breaker (MCB,MCCB,ELCB) for 18.5 kw, 3 ph. 480 v, 60 hz induction motor?