How to know motor winding is star or delta connected without see the information table and winding connection ?
Answers were Sorted based on User's Feedback
Answer / srinivasa rao talasila
Star connected or star running designed motor winding
resistance is some what high compared to delta running
designed motor.
Exambple 5.5KW star designed motor is having a resistance
of 1.2 ohams,same in delta is 0.45 ohams like that
Not exactly the same but there is a difference in
resistance.
| Is This Answer Correct ? | 11 Yes | 6 No |
Answer / k.prakashchandra
If it is LT motor and 3 wires are coming out, it is delta
connected . If there are 6 wires it is neither delta nor
star ,which is decided by starter which connects windings in
star at starting and then in delta afterwards.
| Is This Answer Correct ? | 5 Yes | 3 No |
Answer / gunasekaran
for LT motor if we want more power output it should be delta.for HT motor mostly it should be star connected.some special purpose motor will be delta not all in HT.
| Is This Answer Correct ? | 0 Yes | 1 No |
Answer / goutam roy
In case of star connection, you can have 4nos. Of wire. 3 wires for 3 phases and other for neutral wire (very important for protection) in case of del. Connection you can have 3nos. Of wire. (This connection is very important for arresting harmonic f)
| Is This Answer Correct ? | 0 Yes | 1 No |
Motor star/delta connection = feed by two cable of suitable
core & size.
Motor delta connection = feed by one cable of suitable core
& size.
or
Its application area and load parameters like water
lifting,air-fan in large buildings.
| Is This Answer Correct ? | 2 Yes | 8 No |
How to calculate u.p.s load parsentage plz give me formula
What is the tipical Online UPS input voltage for 20 KVA load ( 3 Phase or 1 Phase )? Why ? Explain it...?
What is star-delta transformer?
On wat basis TSM & PSM are set? Example.TSM=30% n PSM=2.5A....Hw they are set and how we come to know that the particular relay should be set to this value only?
To have variable speeds we use a. Induction motor b. Traction motor c. Shunt motor
how much amps will get from a 360/11kv line
why inverter rating is in KVA
What is dynamo function in DG sets and draw block diagram?
Why space heater is required for each verical bus bar chamber? if one space heater is adequate or not for anti condensation?
In Power cable specification what is U0/U and Um.
Hi Friends pls give information regarding BARC written test. am attending by 20-5-2008. mail me to kkumarei@gmail.com or message to 9962122264
What is the minimum percentage of power that a powerplant can support in ilanding mode ?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)