how many bulb of 60watt at 300volt is used to maintain 0.25
amp.with valid reason?
Answers were Sorted based on User's Feedback
Answer / ashutosh khadgaray
2 coz
P=VICOS(Fi)
60=300*I*0.8
I=.125
0.125 for 1 bulb so for 2 bulb it will be 0.25
| Is This Answer Correct ? | 11 Yes | 3 No |
Answer / ramamurthy
20 of them
4 groups of lamps in series, with each group having 5 lamps
in parallel
| Is This Answer Correct ? | 5 Yes | 1 No |
Answer / kapil joshi
Only 1 Bulb
Because Total Power = 300 * 0.25 = 75 W
Required Power For 2 Bulb =2* 60 = 120 W
which is greater than 75 W
So we can use only 1 bulb
| Is This Answer Correct ? | 1 Yes | 2 No |
If the circuit breaker will not close or it will trip, what will you do?
What is meant by pitch of a synchronous machine.??
CAN WE CALCULATE THE NEGATIVE SEQUENCE AND ZERO SEQUENCE REACTANCE OF A GENERATOR USING ONLY ITS RATED VOLTAGE, KW, PF AND SYNCHRONOUS REACTANCE??? IF YES, THEN HOW??
1. What kVA rating is required for a transformer that must handle a maximum load current of 8 A with a secondary voltage of 2 kV?
Why earthing transformer used in Distribution Sub-Station?
When and where resistance earthing is used ? How to calculate the time constant for earth fault
what is the use of switch disconnector fuse
HOW DOES THE PERCENTAGE DIFFERENTIAL PROTECTION WORK IN POWER TRANSFORMER
what is meant by LT & HT?
What is PMG and AREP excitation system in generator
how do you reduce the skin effect
why generaotr rating is in kva and dc motor in kw?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)