Can we use 11kv Trivector Metre or Energy metre instead
33kv Metre at 33kv Over Head Line metering purpose?
Answers were Sorted based on User's Feedback
Answer / k.prakashchandra
The voltage input to almost all energy meters is 110 V line
to line ,which is the secondary voltage of PTs. You can use
them for all system voltages by applying the correct MF .
| Is This Answer Correct ? | 4 Yes | 1 No |
Answer / mu
we can use any meter at this point as we have to only
change CT & PT's before commissioning,
I have used 11kv meter in 33 kv installation with similar
changes, usual practice done by SEB's across india when
supply voltage changes for any project.
| Is This Answer Correct ? | 3 Yes | 1 No |
Answer / vimal patel
All digital meters can be used at any place like 220kv,66 kv , 33 kv and also 11kv..but first u have to see that metering range of Voltage and Current so u have to adjust that all phase Ct and PT Ratio upto that meter range and than find that MF ( Multiplying factor ) to get Unit.
| Is This Answer Correct ? | 2 Yes | 1 No |
The voltage input to both the meters is 110 V.So, you can
use and pre-set meter constant is to be considered
| Is This Answer Correct ? | 2 Yes | 1 No |
Answer / saleem
The Digital Meter can be used with proper setting, however
the analog meter can not be used because its dial is
calibrated for 11KV.
| Is This Answer Correct ? | 3 Yes | 4 No |
i have old tape recorder speakers(analog).nw i want to use it for my computer system.can i use it to my computer systeno m by using digital to analog converter??? what changes should i do in the system????
what is the working principle of electrical motors?
what do you mean by switchgears?
5 Answers Practical Viva Questions,
what main difference betwenn invetter & ups & major difference
Explain REF protection and sbef protection in transformer?
how many kw = one ton air condition?
if we give 60 hz single phase supply to the transformer used in europe , than what will happen
How could a garment factory benefit from renewable energy
Hod do u calculate cable size for underground laying and the factors effecting/influencing it??
why ct is testing using dc.. y cant we use AC insted of dc on POLARITY TEST.
why transformer ratings in kva? & DG ratings in kva? & Motor ratings in kw/HP?
What is GIS Substation and how it operate? where these type of substation installed?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)