Can we use 11kv Trivector Metre or Energy metre instead
33kv Metre at 33kv Over Head Line metering purpose?
Answers were Sorted based on User's Feedback
Answer / k.prakashchandra
The voltage input to almost all energy meters is 110 V line
to line ,which is the secondary voltage of PTs. You can use
them for all system voltages by applying the correct MF .
| Is This Answer Correct ? | 4 Yes | 1 No |
Answer / mu
we can use any meter at this point as we have to only
change CT & PT's before commissioning,
I have used 11kv meter in 33 kv installation with similar
changes, usual practice done by SEB's across india when
supply voltage changes for any project.
| Is This Answer Correct ? | 3 Yes | 1 No |
Answer / vimal patel
All digital meters can be used at any place like 220kv,66 kv , 33 kv and also 11kv..but first u have to see that metering range of Voltage and Current so u have to adjust that all phase Ct and PT Ratio upto that meter range and than find that MF ( Multiplying factor ) to get Unit.
| Is This Answer Correct ? | 2 Yes | 1 No |
The voltage input to both the meters is 110 V.So, you can
use and pre-set meter constant is to be considered
| Is This Answer Correct ? | 2 Yes | 1 No |
Answer / saleem
The Digital Meter can be used with proper setting, however
the analog meter can not be used because its dial is
calibrated for 11KV.
| Is This Answer Correct ? | 3 Yes | 4 No |
What is the minimum underground tank size capacity considered for firefighting purpose?
what will happen if i connect 12 volt battery with 24 volt battery charger.
why transformer do not rotate?
how to calculate 3 phase clearance in Tower line , 33& 11 KV Line and LT Line.
what are the problems are there if power factor is leading
How to calculate the cable size in sq. mm. when the load is given in KW?
3 shows a 415 V, 3-phase generator supplying a 3-phase 415/110 V transformer. Draw the individual and combined impedance diagrams to a base of 10 kVA. Determine the system fault kVA and the fault currents at the 415 V and 110 V busbars for short circuit faults on the transformer input or output terminals. Work in p.u. values of impedances.
how can we calculate the current
Why we use Electrical energy rather than any other type of energy, mostly? Explain behavior of open secondary CT and short circuited secondary PT in energized condition?
Why we are checking the vector group & turn ratio of Xformer while PM?
Why Magnetic Core Balance test is performed only on Star side of Transformer and not on Delta Side of Transformer (Vector Group Dyn11)?
How to size fuse? How to size MCB?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)