we have consol make 3 phase servo stabilizer for cnc m/c.
while installing the earth neutral voltage is 1.7 volts at
stbilizer off condition and when stabilizer get on en
voltage reaches 4.8 volts (new earthing is done and neutral
is helthy condition all phase to neutral volts 440,442,441
v)why this happen.solution for cause.
Answers were Sorted based on User's Feedback
Answer / vishal ingle
Problem looks like in the type & quality of earthing
electodes and pit specifications. if possible try for
another earthing pit with proper watering arrangement.
Note : the earthing pit should be in mother earth & not in
the backfilled soil. (Earthing quality varies with the soil
strata i.e. BC Soil, Hard rock soil, Muroom etc)
Further the earthing pits may be interconnected also to
obtain stabilised results.
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / k.prakashchandra
There is a slight loose connection/joint in the neutral wire
if the line voltages are equal.
| Is This Answer Correct ? | 0 Yes | 0 No |
plz check your multimeter. it may be because of corrupted
meter. OR while u measure the voltage keep it away from
Electrical area.
| Is This Answer Correct ? | 0 Yes | 1 No |
if vcb make contact but output notreach give the reason?
what is the string efficiency
why frequency meter is connected in parallel in a circuit?
1 Answers University of Engineering and Technology,
Comparision of Air break circuit breaker, SF6 Circuit breaker and vacuum circuit breaker.
which cable is preferred PVC OR XLPE for voltage from 220V to 11 KV with proper justification
we have one ups its neutral is not earthed.its one distribution MCB has a earth fault.but we can not put off any MCB.so how to find out that in which circuit is earthed without isolating the breaker.
Is it recommended to apply H.pot test for new cables segments after terminations or joints, however, this cable has been tested before at the manufactor by the vendor ? or only we can apply megger tests ?
How to design a Unit auxiliary transformer for a power house having a unit of 65 MW and Generating voltage of 11 KV and Secondary voltage of 433V
is it necessarry to charge the battery of ups always??
explain me the relation between torque, frequency,speed,voltage and current in the 3 phase induction motor?
What is mimimum di -electric strength value for 33 KV transformer OLTC oil
why Y CONNECTION IS BETTER INTERMS OF EFFICIENCY AND P.F FOR A LAOD LESS THAN 40% AND WHY AFTER DELTA IS BETTER FOR > 40%
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)