we have consol make 3 phase servo stabilizer for cnc m/c.
while installing the earth neutral voltage is 1.7 volts at
stbilizer off condition and when stabilizer get on en
voltage reaches 4.8 volts (new earthing is done and neutral
is helthy condition all phase to neutral volts 440,442,441
v)why this happen.solution for cause.
Answers were Sorted based on User's Feedback
Answer / vishal ingle
Problem looks like in the type & quality of earthing
electodes and pit specifications. if possible try for
another earthing pit with proper watering arrangement.
Note : the earthing pit should be in mother earth & not in
the backfilled soil. (Earthing quality varies with the soil
strata i.e. BC Soil, Hard rock soil, Muroom etc)
Further the earthing pits may be interconnected also to
obtain stabilised results.
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / k.prakashchandra
There is a slight loose connection/joint in the neutral wire
if the line voltages are equal.
| Is This Answer Correct ? | 0 Yes | 0 No |
plz check your multimeter. it may be because of corrupted
meter. OR while u measure the voltage keep it away from
Electrical area.
| Is This Answer Correct ? | 0 Yes | 1 No |
How to calculate the size of cables (all minium/copper) for a particular load
1 Answers BSL, Galaxy Power System,
WHAT IS THE FUNCTION OF SHORT CIRCUIT MAINTENANCE CT
HOW DOES THE FAN REGULATOR CONTROLS ITS SPEED
This is reqd for a 1MW Solar power plant..We have 2DC outputs from the solar panels Connected to 2INVERTOR panels.. Output from invertor is 3ph,280v,500kva,50hz.These are connected to individual ACB.This has to be stepped up to 11KV ,1250KVA SYSTEM.Now can I use (1) one more ACBTO GIVE A COMBINED OUTPUT OF 1000KVA,280V & STEP UP THE OUTPUT BY USING a single two winding 3 ph transformer 11kv/1250kva. or (2)use the two outputs and connect to one three winding transformer of above rating..Pls suggestwith details.
My meter ratio is -/5 and ct ratio is 100/5 now what will be the multiplying factor and how ?
from which formula we select a capacitor rating?
What are the different towers used in 132kv transmission line? what are the differences between the P,R,S towers used in 132KV and detailed explanation
what happens to a turbo alternator if it get trip and 1 out of 3 poles of circuit breaker in close condition
When do you use a VFD motor?
i need online ups battery calculater
when current lags behind voltage how does it affect the circuit.In other words what is the significance of lagging current?
What will be advantage if we put some load in neutral of grounded star transformer & loadshortcircuit current,rated current of cable & MCB with example?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)