Transformer rating=> 15/20 MVA.Why there are two raings? What
should be the rating of the fuse at the secondary if the
voltage level is 13.8KV/4.16KV?
Answer / k.prakashchandra
15 MVA for one type of cooling and 20 for a better cooling
method.e.g. ON AN and ON AF or OF AF.Current is too high to
use fuses on LT side
Is This Answer Correct ? | 10 Yes | 8 No |
What is the Ramping rate of Generator. What mena Ramping rate
hoW to select a CT?
how single phase preventer works ?
what is difference between elr and R eartl realy.
what is the clearance time circuit breakr?
why we use only sine wave in ac why we do not use other wave forms
what & how to check the lightning arrester
why do we connect voltmeter in parallel,why not in series,and why do we connect ammeter in series why not in paprallel...
what is the difference between inverter and ups & what is the earth resistance for ups , if its high why so
some practicle study shows that the reactive power at the receiving end is not equal to the reactive power at the sending end.But according to theory the reactive power is exchanged by different parts of the network – capacitors and reactors permanently, but is never consumed or produced. Then Where that reacrtive power loss occuring?is there any formula to calculate reactive power loss?