What is the difference between XLPE & FRLS cables? Is FRLS
cables is a type of XLPE cable or both r different?

Answers were Sorted based on User's Feedback



What is the difference between XLPE & FRLS cables? Is FRLS cables is a type of XLPE cable or bo..

Answer / ramesh chandra dhing

XLPE-crosslinked polyethylene.
FRLS-fire retardent low smoke.
FRLS: is a property and its add on feature which is
introduced during manufacturing of cable on demand by which
we can use these cables in fire prone areas and in case of
fire these cables dose not catch fire upto prescribed temp.
level however XLPE is a type of insulation of cable which
improves current carrying capecity of conductor by 5~10%.

Is This Answer Correct ?    77 Yes 4 No

What is the difference between XLPE & FRLS cables? Is FRLS cables is a type of XLPE cable or bo..

Answer / rahul sharma

XLPE is an INSULATING Material while FRLS is a Property
which we seeks in Outer Sheath Part of the Cable. Hence, we
can not compare the Both.

If we are talking about Normal XLPE Cable v/s FRLS XLPE
Cable, then please NOTE that the FRLS XLPE Cables are used
in the Fire Prone Area like Hospitals, Electrical Shops,
Fire Crackeer's Shop.

FRLS Properties:
1. Oxygen index: 29 min, when tested as per ASTM D 2863.
2. Temp. Index: 250°C min,when tested as per ASTM D 2863.
3. Smoke density rating:60% Max,when tested as per ASTM D
2843.
4. Acid Gas generation: Maximum 20% by weight, when tested
as per IEC 60754-1.
5. Flame retardant test as per IEC 60332-3 Cat C will pass.

Above are the properties for FRLS Cables.
** For More information Call me at
rahul.ravincables@gmail.com **

Is This Answer Correct ?    51 Yes 1 No

What is the difference between XLPE & FRLS cables? Is FRLS cables is a type of XLPE cable or bo..

Answer / amit khamesra

XLPE means Cross Linked Poly ethylene cables which may be
FRLS or ordinary. FRLS are fire resistant cables which are
used at the locations which are more prone to fire.

Is This Answer Correct ?    26 Yes 12 No

What is the difference between XLPE & FRLS cables? Is FRLS cables is a type of XLPE cable or bo..

Answer / vinod bisht

actually both are different material where FRLS are used in
fire pron areas and XLPE elsewhere.
XLPE-crosslinked polyethylene.
FRLS-fire retardent low smoke.

Is This Answer Correct ?    17 Yes 9 No

What is the difference between XLPE & FRLS cables? Is FRLS cables is a type of XLPE cable or bo..

Answer / shiva reddy

XLPE means Cross Linked poly Ethylene these cables we are
using in Transmission the AC Supply like 440V

FRLS : Flame Retardent Low Smoke These cables we are using
in Fire panel wiring and smoke detectors wiring and FM 200
wiring and for access contol wiring also
In these cables we transmit DC Supply of 12v to 24V and
size of 0.75 to 1.5Sqmm with steel armoured

Is This Answer Correct ?    14 Yes 15 No

Post New Answer

More Electrical Engineering Interview Questions

What is polarisation index value?.(pi value) Simple & brief definition of polarisation index?..

7 Answers  


Mathemetical Relation Between KWRH and KWH?

3 Answers   UPPCL,


active elements are those which are capable of

2 Answers  


Why field rheostat is kept in minimum position while armature rheostat at maximum position?

0 Answers  


Why only 1 CVT in Y-phase is used for synchronization in 3 phase power system?

1 Answers   Reliance,






WHAT IS MEANT BY BTU OF AIR CONDITIONERS.

2 Answers  


why we are using DC violtage for testing of cables....which is used in HV AC applicatons...

1 Answers  


why master trip(86) used in eletromagnet?

1 Answers  


1)Why potential transformer primary site grounded? 2)can be loop between neutral & body for grounding? 3)What is the difference between ELCB &RCCB? 4)Why we use iron core in transformer insted of wooden core? 5)what is the principle of excitation? 6)Why we test the core balance test for transformer? 7)what is creepage?What is the creepage length for insulators at different voltages? 8)How much type of relays used for differential protection of generator,transformer & busbar protection?

5 Answers  


Our Slip Ring Induction Motor Frequently tripped By Earth Fault While Starting time and in Normal Operation Time also Kindly Let me Know the Reason. Application Ball Mill - Cement Mill

1 Answers  


for 100 HP Induction motor service factor is 1.2(SF) we placed a VFD at the motor side load is balance with 0.3 Amp's Phase to Phase but at incoming of VFD load is un-balance with 10 to 20 Amp's what will be cause of load un balance

0 Answers  


if a 3 phase induction stator has charactristic plate and have on winding inside.with the calculation of plate or dimenssion of core how one can desinge rewinding drawing.

0 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)