what will happen if instead of neutral we use earth wire as
return conductor?if we can use ,then why we are not using in
our day to day appliances?please justify the answer

Answers were Sorted based on User's Feedback



what will happen if instead of neutral we use earth wire as return conductor?if we can use ,then wh..

Answer / guest

If earth is used as return conductor all the earth
protections will b bypassed. If ELCB is used it will not
work and energy meters will not record energy consumed etc.;

Is This Answer Correct ?    19 Yes 8 No

what will happen if instead of neutral we use earth wire as return conductor?if we can use ,then wh..

Answer / rajendra singh

The neutral is a current carrying conductor, but at "ground" potential or close to.
By using the EGC as the neutral, you have neutral current on metal attached to the electrical system. It will and has caused fires and there is the potential for a fatal shock.
For example you use the EGC as the return neutral. An electrican is working on a circuit and opens the neutral and gets a fatal shock.

Is This Answer Correct ?    7 Yes 2 No

what will happen if instead of neutral we use earth wire as return conductor?if we can use ,then wh..

Answer / shamseer m

If connects earth wire instead of neutral wire the equipment will work no doubts, and the voltage given to the equipment (example, a bulb) is same as the voltage given by the neutral wire. even though why we couldn't connects so ???

It is because if we connects earth wire instead of neutral wire the phase(live) voltage will come to the next point of the equipment (in the point where earth wire is connected) via equipment, ie if we use a tester both side of the equipment shows lighted tester.

It can cause electrical shock and damages other equipments by other means.

Is This Answer Correct ?    7 Yes 3 No

what will happen if instead of neutral we use earth wire as return conductor?if we can use ,then wh..

Answer / vivek

we can use earth wire instead of neutral but the potential
difference may decrease because of earth resistance.we are
not using in day to day appliances because if we use earth
as neutral then there is a risk of electric shock

Is This Answer Correct ?    8 Yes 6 No

what will happen if instead of neutral we use earth wire as return conductor?if we can use ,then wh..

Answer / lalu k b

I realised that.. No one have the capacity to explain the answer well...I feel shame..

Is This Answer Correct ?    2 Yes 0 No

what will happen if instead of neutral we use earth wire as return conductor?if we can use ,then wh..

Answer / ranadhir

If we use earthwire instead of neutral what will happen ??
Step potential appear between the feet ,may be around 5volt & a very small current ( mA ) will flow that human body may not feel.
Now in case of fault, fault current will flow to earth & human body standing on floor experience a shock because of rise of step voltage.
So in this case step & touch voltage is dangerous for survival.

Is This Answer Correct ?    0 Yes 0 No

what will happen if instead of neutral we use earth wire as return conductor?if we can use ,then wh..

Answer / naresh

It Will take more power, or draw more current

And energy meter do not record

Is This Answer Correct ?    2 Yes 6 No

what will happen if instead of neutral we use earth wire as return conductor?if we can use ,then wh..

Answer / arunavasudevan

using of earth instead of neutral will damage sometimes all ur appliances....it is dangerous to use.....use only earth as connectivity from neutral

Is This Answer Correct ?    0 Yes 5 No

what will happen if instead of neutral we use earth wire as return conductor?if we can use ,then wh..

Answer / ajaz

uncontrollable current will flow through equipment which is harmful. 

Is This Answer Correct ?    0 Yes 5 No

what will happen if instead of neutral we use earth wire as return conductor?if we can use ,then wh..

Answer / anil

if earth wire is used instead of Neutral wire. Earth wire is
-ive infinit voltage. Then increase in the effective voltage
and then more current will pass. our appliances are meant
for specific voltage grade. this high current will damage
our appliances. usually, you can prove it by using electric
bulb neutral connected with earth wire. and chk the parameters.

Is This Answer Correct ?    4 Yes 10 No

Post New Answer

More Electrical Engineering Interview Questions

what are the interview question asked in wind mill about electrical

0 Answers  


We use ungrounded DC system (220V/110V) for control and protection system in substations etc. Suppose we have long 2 core DC cables running from our DCDB in control room to the load (length of around 2 to 3 km). Do we need to protect these long DC cables from earth leakages or not? If yes how?

5 Answers   Siemens,


what is package substation.how many types they have

0 Answers   ABC,


In a Tap changing transformer where is the tap connected , is it connected in the primary side or it is connected in secondary side

8 Answers   Indiabulls,


What quedtion to ask a electrical maintenance technician?

5 Answers   Bhel, Royal Furnishers,






what is meant by LCR meter? where its useful ?

0 Answers  


ASTM D 3455 - Standard Test Methods for Compatibility of Construction Material with Electrical Insulating Oil of Petroleum Origin has been used for Testing Transformer Oils with a product placed in it. Aged Control Oil has a Power Factor of 0.032% at 100°C. Aged Oil with a Test component has a Power Factor of 0.093% at 100°. Is this increase acceptable? If not why? How much increase is acceptable?

0 Answers  


What is the difference between PLC & DCS?

1 Answers   Power Plant,


HOW TO CALCULATE THE WIRE SIZE FOR THE GIVEN LOAD?

5 Answers  


i am BSEE student, my project study is to synchronize the generator of an hospital, it have a one 313KVA standby-power diesel gen.,and three 100kva transformer.The generator system is operated manually and no ATS or UPS. one more new building is being build so the transformer will be upgrade to a higher vale. 1)how i can connect the new gen. to the old gen. and to the synchronize panel? 2)what is the new gen. to be buy?(rating, etc.) These is my title: To synchronize the generator system of the ____ Hospital. Anyone have a good title? Thanks.

1 Answers  


Control cables in S's will carry 1000v which is AC R DC? Pls answer me 

0 Answers  


What are the electrical engineer roles and responsibilities in chemical plant?

0 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)