Answer / guest

If earth is used as return conductor all the earth
protections will b bypassed. If ELCB is used it will not
work and energy meters will not record energy consumed etc.;

Is This Answer Correct ?    19 Yes 8 No

what will happen if instead of neutral we use earth wire as return conductor?if we can use ,then wh..

Answer / rajendra singh

The neutral is a current carrying conductor, but at "ground" potential or close to.
By using the EGC as the neutral, you have neutral current on metal attached to the electrical system. It will and has caused fires and there is the potential for a fatal shock.
For example you use the EGC as the return neutral. An electrican is working on a circuit and opens the neutral and gets a fatal shock.

Is This Answer Correct ?    7 Yes 2 No

what will happen if instead of neutral we use earth wire as return conductor?if we can use ,then wh..

Answer / shamseer m

If connects earth wire instead of neutral wire the equipment will work no doubts, and the voltage given to the equipment (example, a bulb) is same as the voltage given by the neutral wire. even though why we couldn't connects so ???

It is because if we connects earth wire instead of neutral wire the phase(live) voltage will come to the next point of the equipment (in the point where earth wire is connected) via equipment, ie if we use a tester both side of the equipment shows lighted tester.

It can cause electrical shock and damages other equipments by other means.

Is This Answer Correct ?    7 Yes 3 No

what will happen if instead of neutral we use earth wire as return conductor?if we can use ,then wh..

Answer / vivek

we can use earth wire instead of neutral but the potential
difference may decrease because of earth resistance.we are
not using in day to day appliances because if we use earth
as neutral then there is a risk of electric shock

Is This Answer Correct ?    8 Yes 6 No

what will happen if instead of neutral we use earth wire as return conductor?if we can use ,then wh..

Answer / lalu k b

I realised that.. No one have the capacity to explain the answer well...I feel shame..

Is This Answer Correct ?    2 Yes 0 No

what will happen if instead of neutral we use earth wire as return conductor?if we can use ,then wh..

Answer / ranadhir

If we use earthwire instead of neutral what will happen ??
Step potential appear between the feet ,may be around 5volt & a very small current ( mA ) will flow that human body may not feel.
Now in case of fault, fault current will flow to earth & human body standing on floor experience a shock because of rise of step voltage.
So in this case step & touch voltage is dangerous for survival.

Is This Answer Correct ?    0 Yes 0 No

what will happen if instead of neutral we use earth wire as return conductor?if we can use ,then wh..

Answer / naresh

It Will take more power, or draw more current

And energy meter do not record

Is This Answer Correct ?    2 Yes 6 No

what will happen if instead of neutral we use earth wire as return conductor?if we can use ,then wh..

Answer / arunavasudevan

using of earth instead of neutral will damage sometimes all ur appliances....it is dangerous to use.....use only earth as connectivity from neutral

Is This Answer Correct ?    0 Yes 5 No

what will happen if instead of neutral we use earth wire as return conductor?if we can use ,then wh..

Answer / ajaz

uncontrollable current will flow through equipment which is harmful. 

Is This Answer Correct ?    0 Yes 5 No

what will happen if instead of neutral we use earth wire as return conductor?if we can use ,then wh..

Answer / anil

if earth wire is used instead of Neutral wire. Earth wire is
-ive infinit voltage. Then increase in the effective voltage
and then more current will pass. our appliances are meant
for specific voltage grade. this high current will damage
our appliances. usually, you can prove it by using electric
bulb neutral connected with earth wire. and chk the parameters.

Is This Answer Correct ?    4 Yes 10 No

Post New Answer

More Electrical Engineering Interview Questions

How can I calculate the trnaformer effciency at different loading condition?

2 Answers  


WHAT ARE THE SITE TEST APPLIED ON A SURGE ARRESTORS? DO MEGGER TEST APPLIED ON SURGE ARRESTOR? IF YES THEN WHAT ARE THE ACCEPTED IR VALUE REQUIRED FOR SURGE ARRESTORS FOR VOLTAGE LEVEL 11KV, 33KV, 66KV 132KV, 220KV AND 400KV?

5 Answers  


why using touble tube lamp use in factory?

3 Answers   ONGC,


what is 3rd Harmonics? how it is generated in alternator

2 Answers   Aditya Birla,


any one can explain the stages of a knee point which is taken during ct magnetising curve.

0 Answers   Tata Steel Limited,






How to identify the whether its an isolator or Breaker in MDB

5 Answers  


How much minimum insulation required between 11kv/3.3kv transformer windings?

0 Answers   Descon,


I am new guy as an electrical engr. in a 100MW HFO based power project. I am in operations division. I have noticed from last few days, my supervisor sends the last 24 hours energy generation calculation to my plant manager. I have noticed, he calculated last 24 hour's generated energy differences in KWH then he multiplied it with a multiplying factor 960. for example: total difference =2.685 KWH*960= 2577.6 MWH. but he does not not know what is multiplying factor 960?? can anybody explain it??

1 Answers   Orion,


kVA rating of ordinary transformer is increased when connected as an auto transformer because A transformation ratio increased B secondary voltage increased C energy is transferred both inductively and conductively D secondary current increased

0 Answers  


what will happen if synchronous machine rotor fed from single phase ac supply 

0 Answers  


what is the difference between surge arrestor and surge supressor

1 Answers  


What types of high speed CMOS circuits have you designed?

0 Answers   Ansal Housing, IBM, Intel,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4452)
  • Electrical Engineering Interview Questions Electrical Engineering (16637)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)