what will happen if instead of neutral we use earth wire as
return conductor?if we can use ,then why we are not using in
our day to day appliances?please justify the answer
Answers were Sorted based on User's Feedback
Answer / guest
If earth is used as return conductor all the earth
protections will b bypassed. If ELCB is used it will not
work and energy meters will not record energy consumed etc.;
Is This Answer Correct ? | 19 Yes | 8 No |
Answer / rajendra singh
The neutral is a current carrying conductor, but at "ground" potential or close to.
By using the EGC as the neutral, you have neutral current on metal attached to the electrical system. It will and has caused fires and there is the potential for a fatal shock.
For example you use the EGC as the return neutral. An electrican is working on a circuit and opens the neutral and gets a fatal shock.
Is This Answer Correct ? | 7 Yes | 2 No |
Answer / shamseer m
If connects earth wire instead of neutral wire the equipment will work no doubts, and the voltage given to the equipment (example, a bulb) is same as the voltage given by the neutral wire. even though why we couldn't connects so ???
It is because if we connects earth wire instead of neutral wire the phase(live) voltage will come to the next point of the equipment (in the point where earth wire is connected) via equipment, ie if we use a tester both side of the equipment shows lighted tester.
It can cause electrical shock and damages other equipments by other means.
Is This Answer Correct ? | 7 Yes | 3 No |
Answer / vivek
we can use earth wire instead of neutral but the potential
difference may decrease because of earth resistance.we are
not using in day to day appliances because if we use earth
as neutral then there is a risk of electric shock
Is This Answer Correct ? | 8 Yes | 6 No |
Answer / lalu k b
I realised that.. No one have the capacity to explain the answer well...I feel shame..
Is This Answer Correct ? | 2 Yes | 0 No |
If we use earthwire instead of neutral what will happen ??
Step potential appear between the feet ,may be around 5volt & a very small current ( mA ) will flow that human body may not feel.
Now in case of fault, fault current will flow to earth & human body standing on floor experience a shock because of rise of step voltage.
So in this case step & touch voltage is dangerous for survival.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / arunavasudevan
using of earth instead of neutral will damage sometimes all ur appliances....it is dangerous to use.....use only earth as connectivity from neutral
Is This Answer Correct ? | 0 Yes | 5 No |
Answer / ajaz
uncontrollable current will flow through equipment which is harmful.
Is This Answer Correct ? | 0 Yes | 5 No |
if earth wire is used instead of Neutral wire. Earth wire is
-ive infinit voltage. Then increase in the effective voltage
and then more current will pass. our appliances are meant
for specific voltage grade. this high current will damage
our appliances. usually, you can prove it by using electric
bulb neutral connected with earth wire. and chk the parameters.
Is This Answer Correct ? | 4 Yes | 10 No |
How can I calculate the trnaformer effciency at different loading condition?
WHAT ARE THE SITE TEST APPLIED ON A SURGE ARRESTORS? DO MEGGER TEST APPLIED ON SURGE ARRESTOR? IF YES THEN WHAT ARE THE ACCEPTED IR VALUE REQUIRED FOR SURGE ARRESTORS FOR VOLTAGE LEVEL 11KV, 33KV, 66KV 132KV, 220KV AND 400KV?
why using touble tube lamp use in factory?
what is 3rd Harmonics? how it is generated in alternator
any one can explain the stages of a knee point which is taken during ct magnetising curve.
How to identify the whether its an isolator or Breaker in MDB
How much minimum insulation required between 11kv/3.3kv transformer windings?
I am new guy as an electrical engr. in a 100MW HFO based power project. I am in operations division. I have noticed from last few days, my supervisor sends the last 24 hours energy generation calculation to my plant manager. I have noticed, he calculated last 24 hour's generated energy differences in KWH then he multiplied it with a multiplying factor 960. for example: total difference =2.685 KWH*960= 2577.6 MWH. but he does not not know what is multiplying factor 960?? can anybody explain it??
kVA rating of ordinary transformer is increased when connected as an auto transformer because A transformation ratio increased B secondary voltage increased C energy is transferred both inductively and conductively D secondary current increased
what will happen if synchronous machine rotor fed from single phase ac supply
what is the difference between surge arrestor and surge supressor
What types of high speed CMOS circuits have you designed?
0 Answers Ansal Housing, IBM, Intel,