Answer / s bagchi
Step1: convert the kva or kw load into amps by dividing
with the respective voltage & pf in case of kw.
Step2: refer a cable catalogue & derate the current
considering temperature rating factor & group rating factor.
Step3: select a cable size considering the derated current.
at first you need to calculate the min cable size in case
of ht cables considering short time current & the fault
clearing time of the upstream breaker.
Is This Answer Correct ? | 7 Yes | 1 No |
Answer / harshad
First calculate the current.
Eqn for 3phase: Current= Connected load in watt/sqr root of 3*415*pf
Eqn for 1phase: Current=Connected load in watt/230
Select the cable size from the chart with respect to the current.
pf(power factor) is 0.8 or 0.9
Is This Answer Correct ? | 1 Yes | 0 No |
In dc motor starter there is less voltage required for holding contactor that's may why it is called no volt coil. but in ac starter why holding contactor is called no volt coil.
What is slip in induction motor?
15 kva dg set single phase takes 63amp( approximate) while same rating 15kva three phase takes 35amp approximate. why ? and what will be per phase current for 15 kva
why we use 20 KV, 10KA LA on 22 KV Line
What is mean by hot and cold loop testing?
Can we calculate the P.F if we know the only load on alternator .
Why Water motor is not taking a load or pressure while everything is correct. (Note: Motor running properly)
What are the different lines and what are the different types of losses occur on them?
How we calculate the Multiplying Factor of Kwh meter for 3 phase alternator.
what is the function and use of oil filled cables specify its advantages and disadvantages
what is stper motor
0 Answers Bhel, WAPDA Water and Power Development Authority,
What is technical difference between ELCB & ELMCB?