What is AVR in Turbo generator in Thermal power plant?
Answers were Sorted based on User's Feedback
Answer / rohit chandan
The main purpose of Automatic Voltage Regulator (AVR) is to
control the excitation to limit the terminal voltage of
synchronous generator at reference level.The excitation
system of a Turbo generator contains the exciter and the
AVR. AVR acts upon DC Vf that supply excitation to the
synchronous generator.
Is This Answer Correct ? | 30 Yes | 4 No |
Answer / d oldham
The synchronous generators used do not naturally operate at
any particular voltage but the voltage can be adjusted by
manually setting the excitation. However as soon as any
load is put on the generator a different value of
excitation is required. The AVR automatically makes the
necessary adjustment by closed loop control to keep the
generator voltage constant. The operator can manually
adjust the AVR reference to allow connection to a power
system. Once connected to a large power system the AVR
setting determines the reactive power load kVAR on the
generator. A high setting exports kVAR (lagging power
factor) and a low setting imports kVAR (leading power
factor).
Is This Answer Correct ? | 7 Yes | 0 No |
Answer / mohan kumar
AVR is used to maintain the generator voltage the exciter system w.k.t the exciter give excitation to generator field wdg the the output of AVR is fed to exciter and exciter output voltage is converted to DC through RDFR and it feeds the DC volt to generator field WDG
Is This Answer Correct ? | 4 Yes | 0 No |
Answer / raja
Any one have a book 📖 for the fundamental electrical structure of an thermal power plant.... Please send me @rajako0202@gmail.com
Is This Answer Correct ? | 0 Yes | 0 No |
what is the role of MPU in DG set
1 Answers Weltech Engineering,
what is the difference between ac and dc?which one is more efficient?and what r their advantages
How will be the single line diagram of series trip HT breaker? how it works?
For these 2 devices what their power ratings are ? 1) single phase : AC 220V & starting amps 3Amps (i.e. starting torque) and the stabilized amps 2A ... For deep freezer 2) single phase : AC 220V & starting amps 2.7Amps (i.e. including the starting torque of a CRT monitor) and the stabilized amps 1 Amps thanks
our industries ht line so power fluctation(once drop of power please rectify causes
What is the correct procedure to shutdown VCB in 11kv substation.safety and work procedure
How to Calculate KA Rating of Main LT Panel
diff. between star, delta connection?
WHY DG are rated in KVA or MVA ???., but ALL power plants are rated in KW or MW.,,?
Define unilateral circuit?
In single phase ac ups supply when current is measured with tong tester neutral current is found more than phase current.What is the reason?
what is RNG in the DG synchronizing by PLC?