control valve in manual/auto mode huntting checked spring
tention also it is ok.positioner also good condition &
incoming inst air line also constant pr.kindly give us
correct answer?
Answers were Sorted based on User's Feedback
Please check following things:
1. To loose gland packing, due to tight packing, valve may hunt.
2.Check leakage from diaphragm.
3.May be seat or plug loose
4. Check cut marks at feed back linkages.
Is This Answer Correct ? | 3 Yes | 0 No |
Answer / gopalakrishnan.p
Kindly check the following thigs for betterment
1.Loop tune ur controller.(gain value,integral
time,derivative time).
2.Check the cable(connector side ..i,e may be loose
connection).
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / ashish namdev
Kindly check these following :-
1. first check positioner link spring.
2. adjust link assembly.
3. adjust instrument air at valve specified pressure
through AFR.
4. check all parameters and settings in positioner.
5. give auto calibration command and calibrate it.
6. Tune your controller.(gain, PID controlling)
Is This Answer Correct ? | 2 Yes | 0 No |
please check followings:
1-check gland packing if tight then may be loose.
2-If booster relay installed then check its equlizer valve
some time this valve called by-pass valve.The valve may
adjut to approprite position as hunting stop.
3-Check feed back linkage with touch any part of the body.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / imran
First check its feedback link spring if it is ok then
checked its feedback potentiometer by removing it from
positioner with meter.these r main causes that already i
faced.
Is This Answer Correct ? | 0 Yes | 0 No |
Isometric drawings are generated during _________________ phase of a project
What is the relationship between the universal gravitational constant (G) and the acceleration due to gravity (g)?
i m passed my engineering in 2010 in instrumentation and control engineering. my question is can i apply for software jobs or vacancies.??????????? plz give me answer soonnn......
why k factor is important to know in flow transmitter. if we don,t know k factor what will be issue we can face .
1 Answers Flour Tech Engineers (P) Ltd,
How process line mpm calculation is done?
In electronic board one fuse(rating 230v,100ma)showing 2.5 ohms with multimeter,then the fuse is healthy or not.
How to check vortex flow meter is in good condition while we do not having calibration setup?
how to calibrate pressure gauge(we can not able to fixed by pointer screw adjustment and pointer re fixing method)
Foe selecting control valve if i have the min,normal & max data of flow rate,inlet pressure& outlet pressure,inlet tem.&density than how can i assure that these data are correct,pl. let me know if therew there is any method to check it.& also how we assure that the Cv we get from this data is suitable for valve for controlling require flow.
I want to measure level under vaccum by using DP Tx and vaccum vary between -500 to -670 mmHg and process fluid is accetic anhydride if consider process fluid density 1 kg/cm2. how to calibrate Tx ? consider level is 0 to 100 Cm.
how to caluculate flow by using transmitter?tell me plz I am eagerly waiting for your reply..
2 Answers Agi Glaspac, Reliance Power,
i am working in thermal power plant . if temperature transmitter is not showing reading in dcs then how can we rectify the problem?