Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


control valve in manual/auto mode huntting checked spring
tention also it is ok.positioner also good condition &
incoming inst air line also constant pr.kindly give us
correct answer?

Answers were Sorted based on User's Feedback



control valve in manual/auto mode huntting checked spring tention also it is ok.positioner also go..

Answer / aftab ahmed mazari

Please check following things:
1. To loose gland packing, due to tight packing, valve may hunt.
2.Check leakage from diaphragm.
3.May be seat or plug loose
4. Check cut marks at feed back linkages.

Is This Answer Correct ?    3 Yes 0 No

control valve in manual/auto mode huntting checked spring tention also it is ok.positioner also go..

Answer / gopalakrishnan.p

Kindly check the following thigs for betterment

1.Loop tune ur controller.(gain value,integral
time,derivative time).
2.Check the cable(connector side ..i,e may be loose
connection).

Is This Answer Correct ?    2 Yes 0 No

control valve in manual/auto mode huntting checked spring tention also it is ok.positioner also go..

Answer / ashish namdev

Kindly check these following :-

1. first check positioner link spring.
2. adjust link assembly.
3. adjust instrument air at valve specified pressure
through AFR.
4. check all parameters and settings in positioner.
5. give auto calibration command and calibrate it.
6. Tune your controller.(gain, PID controlling)

Is This Answer Correct ?    2 Yes 0 No

control valve in manual/auto mode huntting checked spring tention also it is ok.positioner also go..

Answer / abdul mannan

please check followings:
1-check gland packing if tight then may be loose.
2-If booster relay installed then check its equlizer valve
some time this valve called by-pass valve.The valve may
adjut to approprite position as hunting stop.
3-Check feed back linkage with touch any part of the body.

Is This Answer Correct ?    0 Yes 0 No

control valve in manual/auto mode huntting checked spring tention also it is ok.positioner also go..

Answer / imran

First check its feedback link spring if it is ok then
checked its feedback potentiometer by removing it from
positioner with meter.these r main causes that already i
faced.

Is This Answer Correct ?    0 Yes 0 No

Post New Answer

More Instrumentation Interview Questions

What is the purpose of the analyzer in petrochemical plant?

0 Answers   ENI, Lakshmi Machine Works,


Why shield is not connected at both end.

5 Answers  


In control engg. : Differences b/w 1st order & 2nd order system, graphically & theoretically ?

0 Answers  


State four different types of flow measurement.

4 Answers   ADMA OPCO,


I faced several time siemens ps2 positioner automatically getting Chang in it's set point direction after auto calibration  So is there any causes biside this or  any  permissives ?

0 Answers  


How a conductivity sensor & analyzer work at boiler, whats the principle & science is beyond this,How conductivity sensor sence & convert signal & move toward analyzer & analyzer show reading in percent? also what is temperature compensate option in conductivity analyzer

0 Answers  


Can we place a Control Panel in Hazardous area Group IIC ? If 'yes' then is there any approval required? If 'yes' then there is any specific IP rating or any standard required? If 'Yes' What is MOC of control panel?

2 Answers  


the square root type transmitter r used to which applications

4 Answers   Roche,


What is mean by analytical instrumentation?

0 Answers  


How does work A temperature valve or fv control valve in process plz brief me

0 Answers   Jindal,


please tel me the calibration of pneumatic controler.

0 Answers  


An equipment is certified for EEX, IA, IIC, T6, what do you under stand by this.

3 Answers   ADMA OPCO,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)