control valve in manual/auto mode huntting checked spring
tention also it is ok.positioner also good condition &
incoming inst air line also constant pr.kindly give us
correct answer?

Answers were Sorted based on User's Feedback



control valve in manual/auto mode huntting checked spring tention also it is ok.positioner also go..

Answer / aftab ahmed mazari

Please check following things:
1. To loose gland packing, due to tight packing, valve may hunt.
2.Check leakage from diaphragm.
3.May be seat or plug loose
4. Check cut marks at feed back linkages.

Is This Answer Correct ?    3 Yes 0 No

control valve in manual/auto mode huntting checked spring tention also it is ok.positioner also go..

Answer / gopalakrishnan.p

Kindly check the following thigs for betterment

1.Loop tune ur controller.(gain value,integral
time,derivative time).
2.Check the cable(connector side ..i,e may be loose
connection).

Is This Answer Correct ?    2 Yes 0 No

control valve in manual/auto mode huntting checked spring tention also it is ok.positioner also go..

Answer / ashish namdev

Kindly check these following :-

1. first check positioner link spring.
2. adjust link assembly.
3. adjust instrument air at valve specified pressure
through AFR.
4. check all parameters and settings in positioner.
5. give auto calibration command and calibrate it.
6. Tune your controller.(gain, PID controlling)

Is This Answer Correct ?    2 Yes 0 No

control valve in manual/auto mode huntting checked spring tention also it is ok.positioner also go..

Answer / abdul mannan

please check followings:
1-check gland packing if tight then may be loose.
2-If booster relay installed then check its equlizer valve
some time this valve called by-pass valve.The valve may
adjut to approprite position as hunting stop.
3-Check feed back linkage with touch any part of the body.

Is This Answer Correct ?    0 Yes 0 No

control valve in manual/auto mode huntting checked spring tention also it is ok.positioner also go..

Answer / imran

First check its feedback link spring if it is ok then
checked its feedback potentiometer by removing it from
positioner with meter.these r main causes that already i
faced.

Is This Answer Correct ?    0 Yes 0 No

Post New Answer

More Instrumentation Interview Questions

Isometric drawings are generated during _________________ phase of a project

0 Answers  


What is the relationship between the universal gravitational constant (G) and the acceleration due to gravity (g)?

3 Answers   APPSC,


i m passed my engineering in 2010 in instrumentation and control engineering. my question is can i apply for software jobs or vacancies.??????????? plz give me answer soonnn......

2 Answers  


why k factor is important to know in flow transmitter. if we don,t know k factor what will be issue we can face .

1 Answers   Flour Tech Engineers (P) Ltd,


How process line mpm calculation is done?

0 Answers  






In electronic board one fuse(rating 230v,100ma)showing 2.5 ohms with multimeter,then the fuse is healthy or not.

4 Answers  


How to check vortex flow meter is in good condition while we do not having calibration setup?

4 Answers  


how to calibrate pressure gauge(we can not able to fixed by pointer screw adjustment and pointer re fixing method)

2 Answers   Nestle, Reliance,


Foe selecting control valve if i have the min,normal & max data of flow rate,inlet pressure& outlet pressure,inlet tem.&density than how can i assure that these data are correct,pl. let me know if therew there is any method to check it.& also how we assure that the Cv we get from this data is suitable for valve for controlling require flow.

3 Answers   HPCL,


I want to measure level under vaccum by using DP Tx and vaccum vary between -500 to -670 mmHg and process fluid is accetic anhydride if consider process fluid density 1 kg/cm2. how to calibrate Tx ? consider level is 0 to 100 Cm.

1 Answers   CCC,


how to caluculate flow by using transmitter?tell me plz I am eagerly waiting for your reply..

2 Answers   Agi Glaspac, Reliance Power,


i am working in thermal power plant . if temperature transmitter is not showing reading in dcs then how can we rectify the problem?

8 Answers   TATA,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)