control valve in manual/auto mode huntting checked spring
tention also it is ok.positioner also good condition &
incoming inst air line also constant pr.kindly give us
correct answer?
Answer Posted / abdul mannan
please check followings:
1-check gland packing if tight then may be loose.
2-If booster relay installed then check its equlizer valve
some time this valve called by-pass valve.The valve may
adjut to approprite position as hunting stop.
3-Check feed back linkage with touch any part of the body.
| Is This Answer Correct ? | 0 Yes | 0 No |
Post New Answer View All Answers
wich is coming the first HAZOP OR SIL
What is the difference between working pressure and calibration pressure of a control valve
send me last 5 years questions asked in rrb chennai, for section engineer
What is the advantage of using locally fabricated hook ups over Pre fabricated hook ups in process instrumentation?
For crude application in floating roof tank, how to calibrate a DP Transmitter? How is the floating roof weight considered?
Explain PID controller tuning & any one method used for it.
if in a level tx height is given, how u calculate the ranges of the tx?
What is heating effect?
what are the selections available in configuring a burnout protection of a controller? thanks
How will you test a transistor with a multimeter?
When doing a liquid seal on a differential flow transmitter , most of the time the sealing liquid will be heavier then the process fluid. For wich application will the sealing liquid be lighter than the process fluid if transmitter is mounted below the process line.
why we use 3 wire rtd direct wiring for temperature measurement instead of temperature transmitter like bearing temperature
For crude application in floating roof tank, how to calibrate a DP Transmitter? How is the floating roof weight considered?
How to decrease opening & closing time of on/off valve?
How vortex sensor used for steam flow measurment can be checked on line i.e without taking out from process line.