An 11kv system consisting of an underground cable to a sub
station about 300 meters away was shut down for about 10
hrs. On energising, it tripped off on earth fault about
10---20 mins later 6 times but since than it is not
tripping.its already 3 weeks now. The SPAJ was found to be
fine. what could be the cause.No test had been done to
determine the cause of the trippings till now because of
demand.
Answers were Sorted based on User's Feedback
Answer / k.prakashchandra
If only you had replaced the breaker cubicle and test
charged you would have come to conclusion.If the all 3 poles
do not close almost at the same time and there is a time
gap, the breaker is likely to trip on EFR due to the
unbalanced current in case of 2 OCR + 1 EFR protection
scheme.In such cases it is advisable to test charge on no
load during the second time and confirm the mechanical fault
which is not consistent & does not occur always.
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / pillay
thanks but I had managed to ON the system and remained
energized with some load for a few minutes (10 -20 mins)
before it tripped again on earth fault , it happened 6 times
on (4/6/2011) and till today (13/07/2011) no problem. we
are using ABB spaj oc/ef relay.
Is This Answer Correct ? | 0 Yes | 0 No |
What are options used for earthing the switchgear.
if 15 kv is grounding directly what will happen?
I am an American living in Vietnam and I have recently gotten a refrigerator from Japan and it is rated for 100 vac, but the power here is 220 so I bought a voltage stabilizer it has a 1 kva output rating. Can you please tell me what the amperage is? I'm confused and without a working fridge.
What are difference between earthing switch and earthing truck ? What is the operation philoshopy of earthing truck ? Wht are the component of earthing truck ?
What is error of a measurement?
When the relative speed between the magnetic fields of stator and rotor does is zero under steady state operation?
what is the mager value of star motor and delta motor between phase to ground and phase to phase, and minimum how much should be value ?
the resistance of wire having length X M is R OHEM if i streched the wire to dubble length what will be the resitance
how can service sitting be setted for MCCB?Example for sittings IR (CURRENT RATING),IS(CURRENT STARTING)IO (current operating)?
formula for incomer breaker size calculation of powerfactor correction unit
Why Stabilising Resistor used in REF circuit ?
what is the difference between single phase, 2 phase, and 3 phase in electric meter?