An 11kv system consisting of an underground cable to a sub
station about 300 meters away was shut down for about 10
hrs. On energising, it tripped off on earth fault about
10---20 mins later 6 times but since than it is not
tripping.its already 3 weeks now. The SPAJ was found to be
fine. what could be the cause.No test had been done to
determine the cause of the trippings till now because of
demand.
Answers were Sorted based on User's Feedback
Answer / k.prakashchandra
If only you had replaced the breaker cubicle and test
charged you would have come to conclusion.If the all 3 poles
do not close almost at the same time and there is a time
gap, the breaker is likely to trip on EFR due to the
unbalanced current in case of 2 OCR + 1 EFR protection
scheme.In such cases it is advisable to test charge on no
load during the second time and confirm the mechanical fault
which is not consistent & does not occur always.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / pillay
thanks but I had managed to ON the system and remained
energized with some load for a few minutes (10 -20 mins)
before it tripped again on earth fault , it happened 6 times
on (4/6/2011) and till today (13/07/2011) no problem. we
are using ABB spaj oc/ef relay.
| Is This Answer Correct ? | 0 Yes | 0 No |
what methods are used to improve power factor?
What's voltage?
1 Answers Pakistan Atomic Energy Commission PAEC,
difference between main metering kiosk and check metering kiosk
Why don't we use ground free electricity to avoid electric shock.As birds are do not get shock.
what is the difference between relay and a contactor.
How to calculate per unit impedance of transformer?
State the types of distortions in amplifier?
what will happen when ac is applied resistor,inductor,capcitor?
Three set (each phase contain 2 cable of 400 mmsq CU XLPE AWA) of single core cables are connected to 11 KV motor of 14 MW & the switch gear supplay is taken from 11kv feeder & this supplay taken from 275 KV substation. Problem is one pair cable(L3- 2 cable ) getting very hot & gland melted and damaged in switch gear side. the other two cable haven't any more hot(ambient temp only & L3 haveing 95- 100 Degree C. The same problem happened in 275 KV substation switch gear side also where the supply taken for 11 kv switch gear. But here L2 phese cable had problem. Why it is happening like this?. The cable having temperature different at different location from gland side inthe case of 11KV feeder of 275 kv substation. why ?
Why the symbol of register is "zig zag"
what is Electrical BMS
which one is more efficient, torq, power & ecnomy with the same frame size AC motor / DC motor?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)