why we use only 4 to 20ma other than 0 to 16 ma
Answers were Sorted based on User's Feedback
Answer / vimal
Whether our instrument is in good condition or not, in order
to check that we are using 4ma as a low value. If we use 0
ma, We can't say that whether the problem is in instrument
or in supply panel.Normally, when we not give supply to the
instrument it will show 0 ma. for that, we use 4 ma as a low
value. Moreover we use 4 to 20 ma as a standard output
because to get linear graph. So, we prefer 4 to 20 ma
instead of 0 to 16 ma..
Is This Answer Correct ? | 33 Yes | 2 No |
Please give you attention below:
4 mA 0 %
8 mA 25 %
12 mA 50 %
16 mA 75 %
20 mA 100 %
at the time of no voltage (zero voltage) we get 0 mA
at the time of 24v dc supply we get 4 mA.
IF we keep the range starting from 0 mA we will get 0 mA at
the time of zero voltage & 24 V dc voltage supply which is
technically not good.
If your observation is too good that time you will
find that from above every gap between each other of 'mA'
& '%' the differrences are equally same.
see for mA : 0-4-8-12-16-20 (gap of 4 mA equally)
and see for % : 0-25-50-75-100 (gap of 25 % equally)
This things easily helpful to sort out the problems.
Therfore this STANDARDISATION is Universal.
Is This Answer Correct ? | 2 Yes | 1 No |
Answer / faiyaz ahmad
4 to 20 mA is a analog signal and its continuous signal its allow to 1 to 5 volts in this signal because its drop of voltage its not drop of current that's why its called standard signal its electrical out put of the transmitter.
4 mA is zero
20 mA is hundred
Is This Answer Correct ? | 0 Yes | 0 No |
Because we want to check the tx is damaged or not.If it
will be normal & no process variable applied then we can
get o/p 4mA...if it will damaged then o/p will not show 4
or near about..
Is This Answer Correct ? | 5 Yes | 7 No |
Answer / sandeep varma
the instruments starts responding from 4mA
Is This Answer Correct ? | 0 Yes | 13 No |
p=hdg,please explain these parameters?
Example of dry contacts & wet contacts?
why are use only 4 to 20ma. signal.
HOW TO CALCULATE ACCURACY OF AN INSTRUMENT. WHICH IS COMPITABLE FOR USE.
What is the minimum rating availalbe for weld neck orifice in market?
Can I route 110 VDC and 24 VDC in a same Duct for our Interposing relay cabinet? IF yes or NO Please provide me IEEE Std. for the same. Please i required it on Urgent basis, i need to design IRP Cabinets and we have MCC 110VDC and Our Coil side is 24VDC, Please help as soon as possible.
7. What are tri-state devices and why they are essential in a bus oriented system
how to calculate the temp. of RTD&Thermocouple when we got some mV r Ohms?if anybody has d chart pls mail the chatrs to me...
how to connect the HART protocal with control valves
In s7-200 we use HMI TD-200C , what that C stands for........ plz reply
I want to know the questions asked in ONGC interview(after being selected in the written exam) for Instrumentation branch.Kindly help.
What is the expansion of RADAR? How it works?