what is negative current?
Answers were Sorted based on User's Feedback
Answer / sathish reddy
negative current means the current flows in opposite to the
assumed positive direction
| Is This Answer Correct ? | 20 Yes | 2 No |
Answer / neha
negative current means the current which flows in the
opposition direction of the load being connect across the
supply.
| Is This Answer Correct ? | 6 Yes | 1 No |
Answer / chad
Assume an AC sin supply then when measurement is taken,
then the test instrument used could be crossed over. The
same result however will be as positive. This also assumes
the voltage is in phase with the current. You can not have
negative power. Out of balance phase current and voltage
will mean inadequate supply to the load. Negative current
would need investigating.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / nitin shingade
nagative current means flow due to the holes in which
electron r mojority carrier viseversa
| Is This Answer Correct ? | 0 Yes | 1 No |
Answer / k.linga reddy
the current flows +ve to -ve but when the current flows -ve
to +ve is called negative current.
| Is This Answer Correct ? | 2 Yes | 11 No |
5.WHICH TYPE WELDING PROCESSES USES NON CONSUMABLE ELECTRODE.........
What are the types of earthing? Explain dagramatically.
Megger type of instrument is used to check??
what is v/f control in VFD?
sir What is the different bet'n "Active & passive" sensors
why do we need the body earth?
How to calculate the current of Highpressure Mercury Vapour Lamp?what is the basis?whether we have to consider power factor or not?
How much allowable difference current between on three phases Dear sir, We have a 1870 KW HT motor, 11 Kv supply,FLA-120A,2870 rpm,2-pole squirrel cage induction Motor.And stator is connected in star connection with Liquid resistance stater to limit the starting current.It has coupled with Centrifugal air compressor.My question is it is loading 73% of FLA taking R-phase 86.7 A, Y-phase-85.4A,B-phase- 78.3A.why the B phase current is that much of difference.Is it allowable, or any one tell me how much allowable current.If any method to calculate.
why ct is connected at bushing of transformer ??????????
. The string effcy in AC sys is 80% Then for same power, the string effcy in dc sys is a) less than 80% b) 80% c) more than 80% d) zero
1 Answers Engineers India Limited,
what is the meaning of cable Glanding can you explain brifly?
what is the function of statics switch in ups and tell me parts
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)