What is the difference between eath fault protection &
Restricted Earth fault Protection?
Answers were Sorted based on User's Feedback
Answer / dinesh kumar
In earth fault protection the feeder or drive is protected
against an earth fault.In restricted earth fault protection
the complete winding of transformer or generator is not
protected against earth fault depending upon the value of
resistance connected in neutral grounding.If the earth
fault occure in the part of unprotected portion of winding
the eart fault relay will not trip
| Is This Answer Correct ? | 1 Yes | 1 No |
Answer / srinivas
earth fault protection allows the total fault current passes through the conductors, by this there may be chance of insulation breakdown, leads to machine failure.
restricted earth fault protection consists the resistance in the neutral wore that limits the fault current to certain level (it depends on the value of the resistance being added), there by more safety to the machine and auxiliaries.
| Is This Answer Correct ? | 0 Yes | 0 No |
what is electricity
WHAT IS EXTENDED DELTA AUTOTRANSFORMER? WHERE WE USE THAT?
how to minimize earth resistance upto 2Ω, if the resistance is 6 Ω ?
is it necessary for 200 kva transformer to have marshaling box and cu plate earthing for neutral
if we know Fault level say 25 KA , How to decide busbar size for Distribution network of 1000 Amp Breaker ? Sample Calculation or Farmula Available or not ?
1)we have 1000 cfm Blower,Dia-1Mtr,Velocity of air 94 m/s 2)We have Natural Air velocity 94m/s 3If i Put Wind Mill in natural air ,speed is 94m/s Then it will generate Assume 100kw 4)If i put same wind mill across the Blower,air speed is same 94m/s now the Question is Will it generate 100 kw?
how we decide the require size is this for a known current at fuu load?
My meter CT is 200/5amps Then my electrical meter MF=???please suggest
Single line diagrams for star to delta and DOL starters.
Fantio of tranformer
condition Autotrip facia come on control panel of electrical transmission line?
capacitor is load free component but why ampare meter shows current when capacitor bank breaker close?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)