Answer / dinesh kumar
In earth fault protection the feeder or drive is protected
against an earth fault.In restricted earth fault protection
the complete winding of transformer or generator is not
protected against earth fault depending upon the value of
resistance connected in neutral grounding.If the earth
fault occure in the part of unprotected portion of winding
the eart fault relay will not trip
| Is This Answer Correct ? | 1 Yes | 1 No |
Answer / srinivas
earth fault protection allows the total fault current passes through the conductors, by this there may be chance of insulation breakdown, leads to machine failure.
restricted earth fault protection consists the resistance in the neutral wore that limits the fault current to certain level (it depends on the value of the resistance being added), there by more safety to the machine and auxiliaries.
| Is This Answer Correct ? | 0 Yes | 0 No |
what is the effect when the shunt field winding is opened in dc shunt motor (i) at the time of starting ? (ii) in running condition ?
and gate circuit diagram,amplifier circuit diagram
what is power load and lighiting load?
What is the latest generation of circuit breakers called?
what happens when ac supply is given to the dc motor and dc supply is given to the ac motor?
1.what is the reason for transformer and lightning arrester blast in 33kv system
sir what is the purpose of SF6 in HT breaker and what is the pressure should be maintain in the breaker?
When testing an earthing connection, we use a 60 or 100 candle bulb with a phase connected direct from supply and the other wire to the new earthing provided.If the bulb glows then the earth is ok.Else earth connection is not Ok. So, why dont we can use all the home appliances taking a single wire from the phase and the return connection to Earth instead of return connection to neutral?
why no load characteristics of generator also called as occ
PLEASE INFORM ABOUT THE IDEAL TEST RESULTS OF MAGNETIC BALANCE TEST OF TRANSFORMER 33/11 kv DELTA-STAR T/F
1.What is the difference between isolators and circuitbreakers? 2.What is bus-bar?
how to select the mpcbs and contactor for 3 phase 30 hp star delta motors.for plc control.and tell me the calaculation for future use.
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)