what is the right cable size for 100 hp mpter.
Answers were Sorted based on User's Feedback
Answer / nagarajan a
suitable cable for 100hp motor aluminium 95 sqmm. cupper 70
sqmm... cable size is depends upon the motor full load
current rating...
Is This Answer Correct ? | 13 Yes | 3 No |
Answer / pankaj kulkarni
first of all calculate how much current it will drawn then
u will decide the rating of suitable cable.....
Is This Answer Correct ? | 6 Yes | 0 No |
Answer / devender sharma
65 mmsq. cu cable is suitable for this motor
Is This Answer Correct ? | 3 Yes | 9 No |
Why 30kw 40 hp 4 pole 3ph induction motor over heated?any steps on reduction in heat?
Why PT burnts?
limitation of conductor height on ground when we consider EMC
what is the mean of short circuuit current ( for ex. 50KA)?
2 Answers Weltech Engineering,
What size cable is used for HT cable to the transformer of 630kVA, and the supply voltage is 11kV
I am getting above 60 V as open delta voltage against single phase unit ICT at tertiary delta formed and ICT getting trippped on NDR. ICT tested and found in order. PTs provided on tertiary are tested and in order. what may be the reason?
what difference beetwin phase voltage & line voltage and phase current& line current ?
what will happen at secondary side of transformer if i increase voltage at primary side?while V1*I1=V2*I2 will secondary voltage or current increase?
Is it possible to make 0.75KW motor earthing from MCC panel by using the 1.5 SQMM, 4 core cable, means 3 core for 3 Phases & 1 core for Earth terminal?
In DC current-excitation to transformer, why it sucks more current? Eventhough there is no power transfer between primary and secondary? R is very low so it should suck less current only na thn y its current increases?
Why AC loads wont used in DC input supply? and Why DC loads wont used in AC input supply?
How to calculate the slip ring induction motor rotor current and voltage.