There is 3phase power cable from 1 point to the other point
which is 100m away. Two point equipped with power meter and
recorded 1st point is 205kW while the 2nd is 202kW and each
phase average carry 400amps. To calculate the resistance of
the 3phase power cable, is the formula using will be P=I2R?
Answers were Sorted based on User's Feedback
Answer / pdbhatt69
If total loss in cable is 3 Kw hence it must be devided n
al 3 phases and hence 1 KW loss in one phase, now you can
use frmula P=I*I*R.It comes around 2.083 Milli ohm.
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / shyamkr
i think the current I will be the r.m.s value of current not
he average value and P will be the power loss in the cable.
so the formula P =I(r.m.s)2 * R.then this formula will give
the resistance in the ac circuit.
Is This Answer Correct ? | 0 Yes | 1 No |
How to reduce power factor correction capacitors failure in an industrial environment with vsd and computers usage in the system
In a 3Ph induction motor(old) 6 wires came out from terminal & not mentioned u1,v1,w1,u2,v2 & w2. how can find out the terminals? how can connect to star delta starter??
If we have a 2000kva load,How much kvar capacitors we go to add to improve the power factor at 0.9?pls give the calculation and fully theory?
what is the difference b/w absolute encoder and incremental encoder?
Write masons gain formula.
the grid connection required for a 50 MegaWatt fotovoltaic powerplant is higher or lower than 35kv (high or medium tension)?
why nutral and earthing wire connect with each other in main panel board.
How can we increase the capacity of exixting capacitor bank??????????????? PLS. Help
Why a transformer is rated in kVA and not in kW??
what is the use of CurrentTransformer in AVR ?
how we decide wire gauge for ac or dc coil and what is the basic diff. B/w these two coil?
Does human body can effect the electric shock when stand on Insulated material?